    I'm new to the group, I have a electrical problem at my house, I will give you a bit of history and will try try to keep it short.
    My problem started with an underground cable fault which was tripping at the municipal meter box outside my property, a contractor was assigned to fix the problem, a "thumper fault locator" was called in and the cable was bridged with aluminum cable ? My problem now is that my earth leakage is tripping on my DB precisely every two hours, 33 minutes past the hour, 5-33, 7-33 9-33 etc., I actually stand in front of the DB ready to reset the earth leakage which stays up till exactly two hours time, this has been constant for the last 3 days. this problem was not there before the work was carried out on the supply cable I'm waiting for the contractor to return to look at it but I was wondering if anyone could shed some light on this problem ??
    Regards
    magron

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    To be so consistent on the 33rd minute I very much doubt it will be supply cable.

    It must be something that is on a timer , delay timer to start, and on resetting the earth leakage it begins the countdown for 2 hours before switching on again to only trip and start the cycle.

    On the next trip , leave it tripped for 10 minutes and see if it still trips on the 33rd minute or is it now forward by 10min.

    To me it sounds like a fridge or freezer defrost cycle kicking in , or something similar

  3. Thanks given for this post:

    Dylboy (16-Sep-23)

  4. #3
    New Member
    Join Date
    Sep 2023
    Location
    Alberton
    Posts
    5
    Thanks
    0
    Thanked 4 Times in 1 Post
    Hi GCE,
    The Contractors have just been to fit a temporary cable so will wait and see what happens. Regarding the timing of the trips, as you are aware, load shedding does not always adhere to the timetable, so let's say the load shedding kicks in at 10-15am and comes back on at 12-20pm, I can guarantee that the earth leakage will trip at 13-33, the odd thing is that its always on the odd hour, never an even hour.

  5. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I would try unplugging fridge , freezer etc - Is about the only thing that I can think would be constant
    Does not make sense though to be so consistent

    Do you have ripple relays fitted by municipality for geyser control

    Maybe post a pic of your D/Board , might just see something

    Be interesting when it is eventually tracked down

  6. #5
    New Member
    Join Date
    Sep 2023
    Location
    Alberton
    Posts
    5
    Thanks
    0
    Thanked 4 Times in 1 Post
    Will let you know as soon as power is restored in the area, we had load shedding but now a damaged cable in the area !!

  7. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Hello : )

    Yes I second the fridge or freezer etc. It could be when the compressor kicks in.

    Keep us posted please : )

    Sent from my CPH2197 using Tapatalk

  8. #7
    New Member
    Join Date
    Sep 2023
    Location
    Alberton
    Posts
    5
    Thanks
    0
    Thanked 4 Times in 1 Post
    Quote Originally Posted by Dylboy View Post
    Hello : )

    Yes I second the fridge or freezer etc. It could be when the compressor kicks in.

    Keep us posted please : )

    Sent from my CPH2197 using Tapatalk
    I will keep you posted, I still don't have power due to an area fault.

  9. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Interesting fault.

    You will need to use a process of elimination.

    If this problem persists, you will need to eliminate all your appliances by unplugging them ALL 10 min before tripping time. Remember it doesn't help just switching them off. You need to unplug them so that the neutral is also disconnected. At least then you will know if it's an appliance or not.

    A friend of mine had an earth leakage that would trip at 2am each morning. It took us 3 days by a process of elimination to establish that it was a faulty earth leakage. Replaced unit, problem solved.

    I'm leaning towards agreeing with GCE on this one.

  10. #9
    New Member
    Join Date
    Sep 2023
    Location
    Alberton
    Posts
    5
    Thanks
    0
    Thanked 4 Times in 1 Post
    Well my problem has gone, since the suspected faulty cable was bypassed with a temporary above ground cable the tripping has stopped, I am completly baffled and will probably go to my grave not knowing what the problem was but I would like to thank everybody for their suggestions

  11. Thank given for this post:

    ACEsterhuizen (18-Sep-23), AndyD (19-Sep-23), GCE (18-Sep-23), Gene (19-Sep-23)

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. Oven tripping earth leakage
    By S.A.M. in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 12-May-21, 10:06 AM
  4. Low earth leakage tripping current
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 15-Mar-19, 07:19 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •