    Supply to complex units.

    Why is it that a unit in a complex may not have a TN-CS supply between the stubby and the unit's DB, but a free standing house may ?

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Following on my previous post, the situation is as follows:

    Unit in a townhouse complex has a high earth loop impedance.
    Stubby / kiosk is 30m away on other side of road.

    Tests done at stubby indicate that the fault is between the stubby and the unit.

    Now one could bridge the neutral and earth at the prepaid meter which is situated next to the unit's DB
    which will result in the earth loop impedance being fine, however, this goes against

    7.16.4.2
    From the point of supply to each user or part of a communal installation, the neutral and earth conductors shall be separate conductors.


    The Municipality says it's ok to do a neutral/earth bridge at the meter, so that paving need not be lifted and the road need not be trenched across to replace the cable.

    Who trumps ? SANS 10142 or Municipality ?

    7

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    If it is all municipal cables up to the meter then it is there problem and it would fall outside of the code and be part of there network.

    Problem with just bridging could mean that there is not a good earth or bad neutral - In my opinion better to fix correctly as the fault could just become worse and burn through the live

  4. Thanks given for this post:

    Derlyn (16-Sep-23)

  5. #4
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    How old is the complex?
    Hereby us, a number of the old houses have a 2core cable coming into the house and we had to bridge the neutral and earth to each other to get the houses compliant. Others have no earth connected to the network so we do the same to them.
    The only problem now is that if the neutral fall away from the network the earth becomes alive! That is not good!
    If there was a working earth in the first place, not working now, I would agree with GCE, get it fixed.

Similar Threads

  1. Pump supply connected to City Power point of supply board
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 10-Dec-21, 10:10 AM
  2. Are expensive earth leakage units better than cheaper units
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 06-Dec-20, 05:48 PM
  3. Neighbour in complex could be a stalker!
    By Beancounter in forum General Chat Forum
    Replies: 8
    Last Post: 16-Nov-14, 08:40 AM
  4. Complex factors for medium term strategic planning in SA
    By Dave A in forum Entrepreneurship and Business Management Forum
    Replies: 5
    Last Post: 24-May-13, 11:05 AM
  5. Tax system too complex
    By Dave A in forum Business Finance Forum
    Replies: 0
    Last Post: 07-Sep-06, 06:48 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •