    Morning all

    I know the minimum permissible single phase voltage is 207v. What is it for 3 phase? Is the minimum voltage calculated on 380v,400v,415v? My phone crashed so I lost my 10142 I had on it.

    Thanks

    Sent from my SM-A336E using Tapatalk

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    The equipment shall be suitable for operation on the maximum steady (r.m.s.)
    voltage and overvoltage to which it is likely to be subjected. Equipment shall
    be rated in accordance with the intended application for use on one of the
    following voltages used in South Africa:
    a) A.C. circuits:
    1) standard voltages of
    i) 230 V single-phase,
    ii) 230/400 V three-phase four-wire, and
    a tolerance of ± 10 % on these voltages.
    NOTE For certain equipment it may be necessary to consider the lowest voltage
    that is likely to occur.
    2) declared voltages of 525 V three-phase three-wire is a commonly used
    voltage and the tolerance is ± 5 %.
    NOTE Declared voltage is the voltage declared by the manufacturer up to the
    maximum of 1 000 V.
    SAB

    Sent from my CPH2197 using Tapatalk

  3. Thanks given for this post:

    madscot (30-Aug-23)

  4. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    As Dylboy mentioned 10 %, however you have to take the voltage on site into consideration.

    The sit eI am working on at the moment

    Red = 221
    White = 225
    Blue = 228

    While carrying out tests today the voltage fluctuated more than 10 volts from one DB to the next.

    I have a site where I connected a PQA, the grid voltage ranges from 260 VAC down to 165 VAC, reported to the supplier, they sent a sparkie with a duspol tester to fix the issue. We have had to install online UPS units to stablise the power to prevent damage to the servers.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Similar Threads

  1. Changing 3 phase electric DB to single phase. (Switchover etc)
    By Janbez54 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 05-Jul-21, 07:59 AM
  2. Inverter diagram for one phase on 3 phase installation feeding 2 db’s
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 19-Aug-20, 06:44 AM
  3. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  4. 3 Phase Voltage Problem
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 25-Jan-13, 02:48 PM
  5. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 08-Feb-10, 09:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •