Results 1 to 4 of 4

Thread: Circuit breaker tripping but not EL

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    131
    Thanks
    60
    Thanked 10 Times in 9 Posts

    Circuit breaker tripping but not EL

    Commercial building in Strydom Park JHB that'd had several sparks doing stuff over many years.

    Intermittent 20A CB on socket circuit tripping usually after loadshedding. Earth Leakage doesn't trip.

    Offending CB swopped out for new. Same thing.

    Installed monitoring device on the circuit to see increased amperage and/or warrage. My thinking the trip is caused by amps exceeding CB, or, in the case of low voltage just after loadshedding, an increase in Watts.

    Not picking anything up that should cause a trip.

    As I understand it a CB will trip on excessive amps or a hard short hot to neutral or ground. Or an arc.

    My thinking (and advice needed pls):-
    1) Unplug everything.
    2) Test each socket with ELCB tester
    3) Megger each circuit
    4) Test every appliance çonnected to sockets

    Thoughts?

    Thanks in advance

    Sent from my SM-A226B using Tapatalk

  2. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Replace the breaker with a D or Curve 1 breaker, do look impedance tests at the socket outlets to verify the circuit are correct.

    Fit those those ellies fridge protectors on appliance which you suspect could have high inrush currents. it would be cheaper than doing power quality tests. I normally charge R10 000 just to take the fluke 435 out the case.

    if it still trips then get a PQA and set it to transients/inrush and switch off/on.




    Quote Originally Posted by Andrew_van_Zyl View Post
    Commercial building in Strydom Park JHB that'd had several sparks doing stuff over many years.

    Intermittent 20A CB on socket circuit tripping usually after loadshedding. Earth Leakage doesn't trip.

    Offending CB swopped out for new. Same thing.

    Installed monitoring device on the circuit to see increased amperage and/or warrage. My thinking the trip is caused by amps exceeding CB, or, in the case of low voltage just after loadshedding, an increase in Watts.

    Not picking anything up that should cause a trip.

    As I understand it a CB will trip on excessive amps or a hard short hot to neutral or ground. Or an arc.

    My thinking (and advice needed pls):-
    1) Unplug everything.
    2) Test each socket with ELCB tester
    3) Megger each circuit
    4) Test every appliance çonnected to sockets

    Thoughts?

    Thanks in advance

    Sent from my SM-A226B using Tapatalk
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  3. Thanks given for this post:

    Gene (05-Sep-23)

  4. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    It could be that the specific circuit powers up equipment which has rectifiers and smoothing capacitors.
    Check what type of equipment is connected on this circuit. VSD drives, Inverter aircons, etc.
    During load shedding, the respective capacitors completely discharge, then at the end of load shedding, when the power comes back, the high inrush current as all the capacitors charge up, will cause the circuit breaker to trip.
    When you switch the breaker off then on again this does not trip as the time may be too short to discharge the capacitors completely as per a load shed cycle.
    Most equipment that has this type of issue has a built in in rush current controller, however this may have failed and hence what you are experiencing.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. Thank given for this post:

    Andrew_van_Zyl (13-Sep-23), Gene (05-Sep-23)

  6. #4
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    43
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi, I would think that after load shedding the diversity factor is out the window and any mcb might tripp including main mcb.

    Sent from my R1PLUS_1 using Tapatalk

Similar Threads

  1. Which Circuit Breaker to use 3KA or 6KA?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Jul-23, 11:56 AM
  2. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  3. Circuit breaker compliance
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Jul-20, 12:53 PM
  4. Circuit Breaker faulty?
    By Melchior in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 09-Mar-17, 11:18 PM
  5. Circuit Breaker tester
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 1