I got a client that had a 14kW Sunsynk inverter installed with batt , solar the lot, he requested a COC for the house wiring as it trips when eskom power comes back on everytime, and that he got a COC from the installer for the solar so no worries here.
Now a quick test and i found that when eskom is down the live and earth measures 78 Volt and neutral and earth measures 97 volt...!!! . as i know that the sunsynk has a automatic neutral earth switch when in operation ,this one does not work or is not set?, or i have to install a neutral earth relay - i requested that he contact the installer, but he asked me to get this system in operation , so here is a case where the fly by night made his money and is gone, this is the second time i had to fix others problems on inverters that was installed by FBN... and also supplying a COC...