    3phase Earth leakage and inverter

    Hello : )

    So now the second time I have seen this.

    Basically the red and yellow phase supplies grid power to the non essentials, then the Blue is from the inverter.

    However they have it all in 1 x 4 pole earth leakage.

    You will see in the picture how there are now two neutral conductors at the top of the earth leakage as one is from Gris main neutral and the second is the neutral from the inverter.


    So now basically it is one earth leakage for both grid and inverter supplies circuits and no splitting of neutral bars.


    I am searching regs and annex P shows split neutral bars and all that. But that is informative and not normative.

    Now I want to change this so the grid which is now a 2 phase be on the 4 pole ELU and then the inverter to have its own 2 pole.

    What in the regs can help me motivate the change. I tried searching split neutrals and 6.12.4 popped up and it confused me a bit.

    Also there is a bunch to do on the DB as you will see in the pic.

    Sent from my CPH2197 using Tapatalk

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Found what was looking for as the inverter only supplies part of the installation.

    7.12.3.1.4 Where only part of an installation is switched to the alternative
    supply in the same distribution board, the neutral bar shall be split (see
    figures P.2 and P.3).

    Sent from my CPH2197 using Tapatalk

Similar Threads

  1. [Question] Earth leakage
    By mnisi3538@gmail.com in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 15-May-23, 11:28 AM
  2. Earth leakage trip on switching over inverter to main supply
    By Gene in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 14-Jul-22, 06:07 PM
  3. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  4. [Question] Inverter's and earth leakage
    By padayad28 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 11-Jul-15, 09:08 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •