Results 1 to 7 of 7

Thread: 1phase booster pump

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts

    1phase booster pump

    Hello : )

    Got a client who has a JoJo system and booster pump. The booster pump I measured pulls 23amps to start. Then runs at 6Amps.

    Now the issue, it was an existing backup system. A 3kw and lead acids.

    We then added 6panels, a new 5kw growatt and a Dyness 5kwh lithium battery.

    Now in laodshedding when the water taps go on the battery trips out. The battery has a max of 100A discharge (5000watts ) but now when the pump starts it pulls 5200ish amps.

    So not everytine but most times it then trips the battery out as it cuts out.

    So is there a way to make or use a soft start on a single phase motor to reduce start up current at all?

    My apprenticeship time we didn't do very many motors at all and then trade test it was just the basics so I admit I do not know a lot on motors at all. Never had a chance really but alas that is how my cookie crumbled.

    So if there is an item I can look at to reduce start up of the single phase please let me know or if there is any other trick to reduce start up.

    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Install a soft start that is designed for single phase pumps

    Do not put a motor on an inverter without a softstart unless the inverter is rated at 8 to 10 times greater than the pump running amps and has no other load .

    On the pumps that have the pressure flow control system you need to fit the soft start between the controller and pump as the controller cannot take the ramp up voltage/frequency from the soft start

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Quote Originally Posted by GCE View Post
    Install a soft start that is designed for single phase pumps

    Do not put a motor on an inverter without a softstart unless the inverter is rated at 8 to 10 times greater than the pump running amps and has no other load .

    On the pumps that have the pressure flow control system you need to fit the soft start between the controller and pump as the controller cannot take the ramp up voltage/frequency from the soft start
    Great thank you ! I think it has a pressure control, will see if I took a decent pic. Thank you

    Sent from my CPH2197 using Tapatalk

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    You would need to connect the softstart between the controller and pump

    Other option is to buy a Dab variable speed pump

    A soft start is in the region of R2,5K

  5. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Perfect thank you : ) appreciate it ! Will look for a soft start, sent an email to one company and then I think electro mechnica also do it

    Sent from my CPH2197 using Tapatalk

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Softstart would definately work but they're expensive. Also look at an NTC as an option, similar to these

    @justloadit I see a business opportunity here for you to produce some off the shelf items for inrush current limiting on pool pumps and wellpoints/borehole pumps etc...
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    Justloadit (25-Jul-23)

  8. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    We have 24 000 BTU aircon units (12 amps max) now plugged into a socket outlet on the essential supply, we use to install 4 mm wire with a dedicated isolator.

    The new 24000 units come pre wired with 1.5 mm catyre and a plug top.

    No more dimming/flickering the lights
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Similar Threads

  1. [Question] Wiring of pump controller
    By viljoenp in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 02-Apr-19, 04:41 AM
  2. Pump with Pressure Tank ???
    By tec0 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 03-Nov-13, 10:52 AM
  3. looking for a 3G booster / repeater
    By SilverNodashi in forum Technology Forum
    Replies: 1
    Last Post: 29-Dec-10, 01:22 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •