Results 1 to 10 of 10

Thread: Bonding (grounding) solar panels

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Quick one, if we bond are we bonding all the metal of the PV and then taking a cable to the Earth of the municipality. I.e the main earth bar of the AC DB board ?

    If so are we now bonding AC and DC so if there is an Earth fault the panels will now be with the AC potential.

    If the above is correct...

    What if it is a ground mount system, now the metal frame is at a higher potential to true earth so if you standing on the earth and touch this now risen above earth potential PV panel you will be shocked ?


    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dylboy View Post
    Quick one, if we bond are we bonding all the metal of the PV and then taking a cable to the Earth of the municipality. I.e the main earth bar of the AC DB board ?

    If so are we now bonding AC and DC so if there is an Earth fault the panels will now be with the AC potential.

    If the above is correct...

    What if it is a ground mount system, now the metal frame is at a higher potential to true earth so if you standing on the earth and touch this now risen above earth potential PV panel you will be shocked ?


    Sent from my CPH2197 using Tapatalk
    Earth is earth - How do you test if your earth is good - You test to the " god made earth" and your " man made earth" and if you get 0 Ohm you have an excellent earth - You reference is the earth , the soil that you stand on and plant flowers in

    If your ground mount system is metal and the poles are buried in the earth then it is more than likely going to have a good earth and the frame cannot be at a higher potential than the earth as it will be at the same potential because it is in the earth - The only time it can be at a higher potential is if the earthing is not good.

    There is no such thing as DC earth and AC earth - It is all earth

Similar Threads

  1. Grounding, earthing and lightning protection for solar panels
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 06-Jan-24, 11:28 AM
  2. Earthing/bonding PV panels
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 25-Apr-23, 12:39 PM
  3. Installing solar panels
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 52
    Last Post: 07-Jan-23, 10:52 PM
  4. Finally, solar panels
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Nov-22, 03:47 PM
  5. Solar panels with a difference
    By Isetech in forum Energy and Resource Conservation Forum
    Replies: 2
    Last Post: 05-Jun-22, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •