    Inverter Islanding?

    I have a Luxpower 5 kVa inverter connected with a battery and solar panels.
    My question is when there is loadshedding the inverter works fine and shows no errors , but on some LED lights that is unswitched shows a glow? after testing live to earth (on inverter output) i get 44 volt, and neutral to earth 37 volt, L to N 230 Volt, now all earth wiring is connected throughout the system to main DB, i also asked the agents on a relay switch for earth neutral connection but they insist it is not necessary and only to earth the system?
    Anyone in the know to fix this?

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    I would start by doing a wore bridge of the inverter output neutral to earth and test again. If it is then 0V between N and E then I would add a relay to bond it only in grid failure. Much like the Sunsynk.

    Sent from my CPH2197 using Tapatalk

  3. Thanks given for this post:

    Gene (07-Jul-23)

  4. #3
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    32
    Thanks
    37
    Thanked 0 Times in 0 Posts
    Thanks, yes it does work and is now connected via a contactor, but the agents insisted that the inverter does have a automatic neutral -earth bridge, this in not what i got, but anyway , im happy as it is legal now.

Similar Threads

  1. Loop impedance tests when in islanding mode
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Apr-23, 06:30 PM
  2. Inverter
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 19-Feb-23, 05:14 AM
  3. 3 KVA inverter
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 01-Apr-22, 04:39 PM
  4. Inverter and UPS
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 07-Oct-21, 01:20 PM
  5. 5 kva inverter
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 14-Feb-21, 10:34 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •