    Inverter/transformer neutral earth connection.

    Hi all
    A friend has a Yamaha generator .
    Internally it has no neutral to earth connection.
    The Earth leakage will not trip when tested with EL tester .
    There is also a polarity fault because one side of the winding is not connected to earth.
    Where is the Protection.
    One cannot connect neutral to earth externally.
    He also has an inverter with the same setup.
    What is the solution.
    Some discussion would be appreciated.
    Thank you




    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    First thing to do is take some voltage readings with a load connected to the generator. L-N ?
    L-E ? N-E ?

    Report back..

  3. #3
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    Once the L-N, L-E, and N-E readings have been taken, a missing Star point will most probably be diagnosed.
    Cheap over-the-counter generators and those bought at Makro and Game very seldom if ever a Star point or like they say "Neutral to Earth bond"
    A star point will have to be created if there is none. Various discussions had been done on which way is best so I'm not going to comment on that issue.

  4. Thanks given for this post:

    Gtfast (05-Jul-23)

  5. #4
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    https://www.theforumsa.co.za/forums/...backup-systems go read that if you have time Very informative

  6. Thanks given for this post:

    Gtfast (05-Jul-23)

  7. #5
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post
    Hi Thanks

    That's the confusing thing.
    I would consider it not a cheap Generator.

    I am still waiting on voltages.

    Why is no neutral earth bond provided.
    The generator is like a safety supply????
    Are we just not buying the correct Generators for house supply.

    I will read further.

    Thanks


    Sent from my CPH2197 using Tapatalk

  8. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Gtfast View Post
    Hi Thanks


    Why is no neutral earth bond provided.
    The generator is like a safety supply????
    Are we just not buying the correct Generators for house supply.
    Yip - incorrect gensets being used from design and then generally also sizing , but in typical South African fashion we make a plan to make it work

    SANS 10142-1
    7.12.2.7 A 230 V generator with a V-O-V earth connection (centre tap on
    winding which is earthed), shall not be connected to a fixed electrical
    installation.
    NOTE Such a generator may be used as a free-standing unit to provide power to
    specific appliances.

  9. Thanks given for this post:

    Gtfast (05-Jul-23)

  10. #7
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post
    Here are the voltages of the generator.

    No load
    L TO N. 232V
    E TO N 3v
    E TO L. 3V

    With 300w load.
    E TO N 11v
    E TO L. 11v

    Not sure about fault current if connecting neutral to earth.Will the generator not get damaged.

    Sent from my CPH2197 using Tapatalk

  11. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Ok. This generator is not vov wound.
    Hopefully it is connected properly through a change over switch. If so, the earth and neutral can be bridged on the generator. I have done this many times with success.

  12. Thanks given for this post:

    Gtfast (05-Jul-23)

  13. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Bridging the neutral and earth will only damage the generator if it is vov wound, which this one according to the voltages is clearly not.

  14. #10
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I removed ad blocker, because Youtube no longer allow registration, it has made this site a terrible experience
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Neutral Earth bonding of inverter
    By JackC in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 07-Sep-23, 08:10 AM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. 230 volt generator with a V-O-V earth connection
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 29-Jul-20, 09:33 AM
  4. Transformer HV EARTH
    By Eskom in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 13-Apr-16, 10:19 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •