    Ripcord

    Hi can anyone point me to the right regulation regarding ripcord supplying a single socket wall plug (fixed to wall) as well as supplying a second double wall plug(also fixed to wall.)
    the second ripcord supplies yet another single wall plug also fixed to wall.
    oh and before i forget both ripcords feed from 1 16A plug top plugged in to original wall socket.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Lourens99 View Post
    Hi can anyone point me to the right regulation regarding ripcord supplying a single socket wall plug (fixed to wall) as well as supplying a second double wall plug(also fixed to wall.)
    the second ripcord supplies yet another single wall plug also fixed to wall.
    oh and before i forget both ripcords feed from 1 16A plug top plugged in to original wall socket.
    being ripcord I assume no earth - That would be the easiest regulations to fail it on - There are many more

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    This gets interesting as it may be considered an appliance.

    However as discussed before if it is physically attached to the house brick and mortar I believe it is part of the electrical installation as it is fixed thus needs to comply with overfurrent and short circuit protection as well as the cable ratings for such and socket circuits not supplied by less than a cable that is rated less than 16amps.

    But keen to find out what others think of it being an appliance or part of the electrical installation as one Dan argue to just un plug it and then no longer part of it.

    While typing a socket can be used as a isolation device so then again it's part of the electrical installation and must comply

    Sent from my CPH2197 using Tapatalk

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dylboy View Post
    This gets interesting as it may be considered an appliance.

    However as discussed before if it is physically attached to the house brick and mortar I believe it is part of the electrical installation as it is fixed thus needs to comply with overfurrent and short circuit protection as well as the cable ratings for such and socket circuits not supplied by less than a cable that is rated less than 16amps.

    But keen to find out what others think of it being an appliance or part of the electrical installation as one Dan argue to just un plug it and then no longer part of it.

    While typing a socket can be used as a isolation device so then again it's part of the electrical installation and must comply

    Sent from my CPH2197 using Tapatalk
    The fixed appliance excuse went out the window a couple of editions ago - In my opinion the 2 regulations pasted below close down the fixed appliance route



    6.16.1.5 A socket-outlet shall supply only one fixed appliance. The use of
    flexible cords of length exceeding 3 m is not recommended. The reason for
    this recommendation is an endeavour to ensure operation of the overcurrent
    protective device. (See also 6.14.1.4 for luminaires).

    6.16.1.10 The wiring between different parts of a fixed appliance that are
    installed separately is part of the fixed installation
    , even where it is supplied
    from a socket-outlet, unless such wiring is less than 3 m in length.
    Such wiring shall be protected by separate overload protection unless its
    current-carrying capacity is such that the circuit protection of the socket-outlet
    circuit will provide protection or that part of the appliance has built-in thermal
    overload protection.
    NOTE Where the length of wiring exceeds 3 m, the impedance and the functioning of
    the protective devices need to be considered to satisfy the overcurrent protection
    requirements in this part of SANS 10142.

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    As pointed out by GCE, take note of 3.3.3.

    3.3.3
    fixed appliance
    appliance that is fastened or otherwise secured at a specific location, and
    that would require the use of tools to be moved to another location

    Quote Originally Posted by Lourens99 View Post
    Hi can anyone point me to the right regulation regarding ripcord supplying a single socket wall plug (fixed to wall) as well as supplying a second double wall plug(also fixed to wall.)
    the second ripcord supplies yet another single wall plug also fixed to wall.
    oh and before i forget both ripcords feed from 1 16A plug top plugged in to original wall socket.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.