    Permanent N/E bond or Relay bond

    I know this has been discussed numerous tines here and elsewhere.
    Can someone confirm or forward a link that states it's regulation to use a contactor OR a permanent bond when in islanding mode?
    I've been using the ATS 230 v relay to switch a contactor to bond earth and neutral.
    Some blokes say what if contactor fails?
    Is it clearly regulations that you cannot make a permanent bond?
    Please advise

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    The inverter output might fail as well. What then ?

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Delta View Post
    I know this has been discussed numerous tines here and elsewhere.
    Can someone confirm or forward a link that states it's regulation to use a contactor OR a permanent bond when in islanding mode?
    I've been using the ATS 230 v relay to switch a contactor to bond earth and neutral.
    Some blokes say what if contactor fails?
    Is it clearly regulations that you cannot make a permanent bond?
    Please advise
    I cannot tell you were it states it must be a permanent bond - I can show you were it states it may not be a permanent bond

    SANS 10142-1 ed3.1
    6.1.6
    The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.


    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together
    (see figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected
    (see also
    6.1.6).

    7.16.4 Neutral earthing
    7.16.4.1 Whereas TN-C systems may be implemented along the distribution
    system backbone, the individual service connections at every distribution
    kiosk shall be TN-S.

    7.16.4.2 From the point of supply to each user or part of a communal
    installation, the neutral and earth conductors shall be separate conductors.

    7.16.4.3 Wherever the neutral is connected to the earth, a warning notice
    shall be fitted to the outside of each distribution kiosk in the distribution
    system, indicating "Neutral earthed inside".
    7.16.4.4 A clear notice shall be fitted at the combined neutral-earth
    connection inside each distribution kiosk in the distribution system, that
    prohibits the removal of this connection while the supply is alive, or might
    become alive.
    7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.
    7.16.4.6 A TN-S system shall not be converted to a TN-C system.

  4. #4
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    not true - misleading at best - this sans 10142 is a joke and the klevva klevvas that pins it down.

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by ACEsterhuizen View Post
    not true - misleading at best - this sans 10142 is a joke and the klevva klevvas that pins it down.
    Which statement is not true in your opinion - permanent or relay

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    That is why I suggested to the inverter manufacturer, that they should make it fail safe and because the inverters are now so smart they could send you a notification indicating that the relay has failed.

Similar Threads

  1. Earth/neutral bond relay size
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 13-Oct-24, 07:54 PM
  2. [Question] Bond arrears
    By ians in forum General Business Forum
    Replies: 69
    Last Post: 02-Feb-24, 08:36 PM
  3. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •