Page 3 of 3 FirstFirst 123
Results 21 to 30 of 30

Thread: Definition of a circuit.

  1. #21
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I sent you a whattsapp with the documents.

    Quote Originally Posted by Derlyn View Post
    Not to open a can of worms, Brother, but how can a COC be valid without section 3 filled in ?
    I'm trying to get my head around that one.

  2. #22
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Thanks brother, received. Thats section 3 and a bit extra. Your post had me thinking. 👍👍👍

  3. #23
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This certainly got me thinking, if you fill out the COC and section 3 the way you are suppose to, with all he correct data, eitehr way you wouldnt have a problem.

    Lets say, there is 2 plug circuit (with 20 or 30 amp circuit breakers depending on the age of the installation and wire size) and 1 light circuit ( with a 5 or 10 or 15 amp circuit breaker) with 2 wires in each.

    Once you count the points it would prevent you from adding circuits to the circuit breaker or electrical installation.

    2 plug circuits and 5 points, if you fill out the document with 4 circuits and 5 points, there are still only 5 points, all you going to do is confuse peopled as pointed out already in this thread, it just doesnt make sense that you would need to remove the cover to identify the amount of circuits, Common sense would tell me that if you are going to count the wires in each breaker as points, then you need to correctly lablel the DB. Plugs P1 and P2, Plug P3 and P4, Lights L1 and L2, you would then need to attach a circuit label to each wire identifying which circuit each wire feeds, then attach a holder to the wall with a site layout of the circuits.

    Considering we have gone from a 4 page COC to a 2 page COC, I cant see this happening any time soon

    The only time counting wires on a breaker would be an advantage, if you are doing comercial/industrial installation where you are provived a site layout with all the circuits identified on the drawing, and even then it wouldnt apply because you could have 2 of the same "circuits" connected to one circuit breaker.




    Quote Originally Posted by GCE View Post
    Just think - Even more incorrectly filled in COC's for you to kick back

  4. #24
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Doing it the way we do, prevents this type of confusion. It also helps when you work on a property where people work from home or in offices where you cant switch off the power just randomly so that you can identify a "circuit" be it a wire of "breaker" and nobody can add "points" nor circuits.

    Just when we thought this was a challenge, there is a new way bigger challenge looming, dedicated/essential/critical circuits, connected to an inverter, this has already proved to be an issue challenge than one would expect.

    We go to all the trouble of separating non essential and essential sometime refered to as critical or dedicated outlets.

    In the past we have always use a special socket outlets (red with a flat section on the earth pin) for dedicated circuits.

    Inverter service centres wonder why they have all these damaged units arriving, with burnt out relays. Nobody thought to fit dedicated outlets and tell everyone on the property about the socket outlets are connecte dand which are not connected to the inverter.



    Quote Originally Posted by Derlyn View Post
    Thanks brother, received. Thats section 3 and a bit extra. Your post had me thinking. 

  5. #25
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Isetech View Post
    Doing it the way we do, prevents this type of confusion. It also helps when you work on a property where people work from home or in offices where you cant switch off the power just randomly so that you can identify a "circuit" be it a wire of "breaker" and nobody can add "points" nor circuits.

    Just when we thought this was a challenge, there is a new way bigger challenge looming, dedicated/essential/critical circuits, connected to an inverter, this has already proved to be an issue challenge than one would expect.

    We go to all the trouble of separating non essential and essential sometime refered to as critical or dedicated outlets.

    In the past we have always use a special socket outlets (red with a flat section on the earth pin) for dedicated circuits.

    Inverter service centres wonder why they have all these damaged units arriving, with burnt out relays. Nobody thought to fit dedicated outlets and tell everyone on the property about the socket outlets are connecte dand which are not connected to the inverter.
    I am glad that my simple little circuit and question, got one or two people thinking.

    I have been counting circuits ever since I can remember and always thought it to be what the test sheet asks for.
    Then along comes someone and questions your method. This causes a little bit of doubt in one's mind.

    Thanks to this forum and the regular contributors, I have now for once and for all put my mind at ease knowing that
    I have been doing what is required, correctly.

    Mission accomplished.

    Now onto the next one ................

  6. #26
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Just make sure you label your DB correctly, indicating the number of circuits the breaker is feeding.

  7. #27
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I keep hearing this phrase, "read the regualtions", so I decided to go read the regs for the millionth time. I also keep hearing "read the instruction manual", the catch with the instruction manual it keeps telling me to read my local code, so why waste time reading the instruction manual, anyway that a discussion for another day.

    "3.11circuit arrangement of conductors (see 3.14) for the purpose of carrying electric current"

    "3.14conductor material that is capable of conducting electric current"

    Is the wire in the bottom of a circuit breaker a conductor or a circuit?

    If you counting the wires as circuits, what happens if you have 2 wires feeding the same group of lights in a room for example?

    Let’s say you have 2 rows of down lights in a lounge or office for example with 6 lights each, would it be number of circuits 2 and 12 points or 1 circuit and 12 points?

    If you add another light at the entrance to the lounge/office and run a wire to the DB and connect it to the same "circuit breaker" which is closer to the DB, do you add another circuit and another circuit and light point?

    How do you label your DB.

    3 X light or lights X 3 or

    lights with X 3 below?

    Do you label each "conductor" connected to the "Circuit" breaker, "circuit" 1/2/3 for easy identification


    lights with a label below 3 circuits ?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  8. #28
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Isetech View Post
    I keep hearing this phrase, "read the regualtions", so I decided to go read the regs for the millionth time. I also keep hearing "read the instruction manual", the catch with the instruction manual it keeps telling me to read my local code, so why waste time reading the instruction manual, anyway that a discussion for another day.

    "3.11circuit arrangement of conductors (see 3.14) for the purpose of carrying electric current"

    "3.14conductor material that is capable of conducting electric current"

    Is the wire in the bottom of a circuit breaker a conductor or a circuit?
    A conductor or a circuit - You actually answered your question with the definitions in the previous sentence .

    A piece of wire lying in your tool box is a conductor - Once you join those conductors in an orderly fashion to achieve a purpose then it will be " carrying Current " and so it will be a circuit or if you prefer an arrangement of conductors


    If you counting the wires as circuits, what happens if you have 2 wires feeding the same group of lights in a room for example?

    Let’s say you have 2 rows of down lights in a lounge or office for example with 6 lights each, would it be number of circuits 2 and 12 points or 1 circuit and 12 points?
    It is 2 circuits as it is 2 separate arrangements of conductors independent of each other , carrying current

  9. Thanks given for this post:

    Derlyn (10-Jul-23)

  10. #29
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Would you agree that each conductor should be labelled to identify that it is a circuit with the circuit number and the DB cover must have the correct labels, identifying that there is more than 1 circuit connected to the circuit breaker and what it feeds?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  11. #30
    Full Member W-TDMI's Avatar
    Join Date
    May 2013
    Location
    George
    Posts
    39
    Thanks
    2
    Thanked 7 Times in 7 Posts
    There is defenitly 2 circuits leaving that DB - you where correct all the years please keep doing it the same.

  12. Thanks given for this post:

    Derlyn (12-Jul-23)

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Definition of distribution board.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 19-Feb-22, 07:56 AM
  2. [Question] Income definition
    By Raene in forum Accounting Forum
    Replies: 1
    Last Post: 24-Oct-13, 06:10 AM
  3. [Question] Tax Practitioner Definition?
    By anon1 in forum Tax Forum
    Replies: 1
    Last Post: 21-May-13, 02:37 PM
  4. Definition of personal service company
    By deweyzeph in forum Tax Forum
    Replies: 4
    Last Post: 09-Jun-12, 06:48 AM
  5. A Quick Question for the HR Folks - What's the Definition of a Calendar Month?
    By rfnel in forum Labour Relations and Legislation Forum
    Replies: 1
    Last Post: 07-Mar-12, 07:35 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •