Page 1 of 3 123 LastLast
Results 1 to 10 of 24

Thread: Neutral Earth bonding of inverter

  1. #1
    Junior Member
    Join Date
    Jan 2023
    Location
    Pretoria
    Posts
    12
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Neutral Earth bonding of inverter

    With reference to my "Inverter Battery Wiring" and other threads related to this topic.

    I decided to go the route of a separate electrical circuit for the output of my inverter, as suggested against the above thread.

    Which means that I will need to bond the Neutral and Earth on the inverter's output before feeding a new DB board. As suggested in one of the threads I will feed from the inverter output to a small box where I will bond the neutral and earth before feeding the new DB board. My inverter is a cheapie bought online (see attachment) but it is working fine. I get the following voltage readings on the inverter's output:
    Between Live and Neutral - 219 Volt, between Live and Earth - 103 Volt and between Neutral and Earth 111 Volt. The earth is connected to the frame of the inverter with a 0.4 Ohm reading.

    Question now; will it be safe to bond the inverter's Neutral and Earth just after the output plug (as explained above)? I tried to contact the distributor but without any success. Your advice/ opinion will be appreciated.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Inverter.jpg 
Views:	201 
Size:	19.3 KB 
ID:	8756  

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    That's a VOV output. You cannot just bridge neutral to earth on that output.

  3. #3
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    I would say the best point would be in the db before the earth leakage

  4. #4
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    There are electrical ready boards available, prewired with plugs, some even have a bulkhead, but most of them don't have a main breaker though.
    You can also buy all the parts and build a db according to your needs
    Good luck with your project

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Question.

    Would it make life any easier for everyone if inverters were manufactured with built in earth leakage relays ?

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Question.

    Would it make life any easier for everyone if inverters were manufactured with built in earth leakage relays ?
    No - Could be a problem with neutral earth bridges , if you running dedicated circuits especially in shops that have cctv alarms etc

    Inverters are also generally made to an international standard and you can choose the different grid set ups according to the country you stay in

  7. Thanks given for this post:

    Derlyn (19-May-23)

  8. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Another question ( sorry )

    Never tried this before.

    On a plug and play inverter where the output is not in any way connected to the the installation ...... if there's a leakage to earth on an appliance plugged in to the output, is there any earth leakage protection ?

  9. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This is the reason the old SABS regulations worked, an inverter like this would never be SABS approved for use in SA to connect to an electrical installation. In this day and age anything goes, some of us try ot hold on to the old ways of doing things, in reality anything goes.

    It would be an interesting to hear if an insurance company would pay out for a claim related to one of these units connected to an elctrical installation.

    Just like the plug and play units, they are not designed to be connected to electrical installation period, but in Sa nobody realy car, desperate times call for desperate measures.

    This neutral/earth bonding fiasco is a good expample of how bad things have got, with a 70 - 30 % in favour of the permemant bond, you can jump up and down till the cows come home, if the AIA says the regs dont apply and their decision rule and the DOl appointed them, who are we to argue ?

    Now there is talk (the key word "Talk"... talk talk talk) of a 400 a page revision to the SANS book, which will include many new rules and regulations, if we cant even get the regs right from the present book hgow will new regulations help?

    The best part is who is going to pay to bring all the hundreds, yes you heard right hundreds of thosands of solar installations already installed, up to standard.

    One of the other interesting issues is going to eb the regisatration of all these units, yes that includes your small inverter connected to the electrical installation. I received a quote for an SSEG to be registered, it was over R10 000 and that doesnt include the council costs.

    We are in for some interesting time ahead.

    There is good news, a stage 10 load shedding schedule has been released, which means more and more work, the smart people who climbed on this band wagon are smiling all the way to the bank

  10. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    Another question ( sorry )

    Never tried this before.

    On a plug and play inverter where the output is not in any way connected to the the installation ...... if there's a leakage to earth on an appliance plugged in to the output, is there any earth leakage protection ?
    Interesting question, in the case that the unit is being fed through the inverter, and an earth fault occurs between Neutral and Earth, then the AC feed side ELU will trip, then the interesting part happens, the inverter will now switch on and supply the load with power. So effectively no earth fault trip.
    Now the second scenario, if there is a Live to earth fault, then the AC feed side ELU will trip, the Inverter powers the load, and depending on the severity of the Live Earth fault, the inverter may or may not trip on an overload condition.

    NOT SAFE!

    So again here is the situation, if you provide the ELU safety on the output side of the inverter, then you are way more expensive than the next fellow who does not care, but sells and makes the sale because he is cheaper.

    Go figure.
    Cost trumps safety to most customers who have no understanding of electricity.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  11. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @Justloadit. Thank you my brother. That was my line of thinking.

    Now to throw a spanner in the works with an inverter that has a vov output such as the one mentiioned above by JackC where an earth leakage on the output means diddly squat. 😂😂

Page 1 of 3 123 LastLast

Similar Threads

  1. Neutral earth bonding on backup systems.
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 145
    Last Post: 24-Mar-24, 04:37 PM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  4. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •