    Neutral Earth bonding of inverter

    With reference to my "Inverter Battery Wiring" and other threads related to this topic.

    I decided to go the route of a separate electrical circuit for the output of my inverter, as suggested against the above thread.

    Which means that I will need to bond the Neutral and Earth on the inverter's output before feeding a new DB board. As suggested in one of the threads I will feed from the inverter output to a small box where I will bond the neutral and earth before feeding the new DB board. My inverter is a cheapie bought online (see attachment) but it is working fine. I get the following voltage readings on the inverter's output:
    Between Live and Neutral - 219 Volt, between Live and Earth - 103 Volt and between Neutral and Earth 111 Volt. The earth is connected to the frame of the inverter with a 0.4 Ohm reading.

    Question now; will it be safe to bond the inverter's Neutral and Earth just after the output plug (as explained above)? I tried to contact the distributor but without any success. Your advice/ opinion will be appreciated.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Inverter.jpg 
Views:	201 
Size:	19.3 KB 
ID:	8756  

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    That's a VOV output. You cannot just bridge neutral to earth on that output.

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by Derlyn View Post
    That's a VOV output. You cannot just bridge neutral to earth on that output.
    Not just a floating neutral?
    Or did you check the specs on the unit?

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Dave A View Post
    Not just a floating neutral?
    Or did you check the specs on the unit?
    The specs on these types of inverters only give the live/neutral voltage output.

    I was probably a bit hasty with my VOV reply. Its just seldom that one measures a floating neutral scenario so close to exactly half the supply voltage. ( possible, but seldom )
    Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs.
    I was under the impression that the author had done this.

    Had he not, it will be interesting to know the outcome after doing so.

  5. #5
    Junior Member
    Join Date
    Jan 2023
    Location
    Pretoria
    Posts
    12
    Thanks
    1
    Thanked 0 Times in 0 Posts
    "Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs"

    I done it with a small hair dryer as load, the voltages remain the same as tested previously. I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp. As explained by various forum members it seems like an inverter developed specifically for mobile use.

  6. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by JackC View Post
    "Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs"

    I done it with a small hair dryer as load, the voltages remain the same as tested previously. I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp. As explained by various forum members it seems like an inverter developed specifically for mobile use.
    Thanks for that feedback brother. Interesting. So it seems as if that inverter has a VOV output.
    Like you say ..... specially made for mobile use.

    Cheers.

  7. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by JackC View Post
    I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp.
    Could the 0.07Amp be an electronic amplifier offset value that is inherent in the clamp meter?
    This can be verified, by reading the display, with the jaws shut before doing the measurement. Some of the Clamp Amp meters do have a 'Zero' button.
    Anyway a Clamp Amp meter with a 40/20Amp range will not read AC milliAmps correctly, as it will be out or range for the specific amp meter range.
    To do these kind of low AC milliamps measurements, one will have to get a high quality, expensive AC Clamp Meter.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #8
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    I would say the best point would be in the db before the earth leakage

  9. #9
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    260
    Thanks
    14
    Thanked 21 Times in 19 Posts
    There are electrical ready boards available, prewired with plugs, some even have a bulkhead, but most of them don't have a main breaker though.
    You can also buy all the parts and build a db according to your needs
    Good luck with your project

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Question.

    Would it make life any easier for everyone if inverters were manufactured with built in earth leakage relays ?

Page 1 of 3 123 LastLast

Similar Threads

  1. Neutral earth bonding on backup systems.
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 145
    Last Post: 24-Mar-24, 04:37 PM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  4. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •