Page 3 of 3 FirstFirst 123
Results 21 to 24 of 24

Thread: Neutral Earth bonding of inverter

  1. #21
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,538
    Thanks
    108
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by JackC View Post
    "Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs"

    I done it with a small hair dryer as load, the voltages remain the same as tested previously. I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp. As explained by various forum members it seems like an inverter developed specifically for mobile use.
    Thanks for that feedback brother. Interesting. So it seems as if that inverter has a VOV output.
    Like you say ..... specially made for mobile use.

    Cheers.

  2. #22
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,491
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by JackC View Post
    I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp.
    Could the 0.07Amp be an electronic amplifier offset value that is inherent in the clamp meter?
    This can be verified, by reading the display, with the jaws shut before doing the measurement. Some of the Clamp Amp meters do have a 'Zero' button.
    Anyway a Clamp Amp meter with a 40/20Amp range will not read AC milliAmps correctly, as it will be out or range for the specific amp meter range.
    To do these kind of low AC milliamps measurements, one will have to get a high quality, expensive AC Clamp Meter.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #23
    Junior Member
    Join Date
    Jan 2023
    Location
    Pretoria
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Leakage Current

    "To do these kind of low AC milliamps measurements, one will have to get a high quality, expensive meter"

    Repeated the test with a RS-Pro Leakage Current Clamp meter. Readings are Live- 2.180 Amp, Neutral- 2.179 Amp and with both live& Neutral together 0.001 Amp (1 Milli Amp).

  4. #24
    New Member HGTesla's Avatar
    Join Date
    Jul 2023
    Location
    China
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Most inverters now these days have the FG or G connection as well as a neutral for internal ground fault protection.This is a standard affair with earth bonded neutral utility installation.
    Last edited by Dave A; 16-Sep-23 at 08:38 AM.

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Neutral earth bonding on backup systems.
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 145
    Last Post: 24-Mar-24, 04:37 PM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  4. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •