    For the VoV one when doing a DB tie or whatever, don't use the earth of the output and then bridge the Neautral and Earth on the "supply side" so basically not shorting the VoV.

    So using the Line and Neutral only from the inverter and joing the out going supply Earth to the Neutral.

    That is how I see it can be done on a VoV.

    Sent from my CPH2197 using Tapatalk

  2. #12
    Junior Member
    Join Date
    Jan 2023
    Location
    Pretoria
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thanks everybody for your contributions. I will try to digest the information and try to come up with possible solutions.

    I anyway decided not to bond neutral and earth on the output of the inverter, therefore I will keep my trolley as a portable solution. But I will try to make it as save as possible by introducing an ELU.

    Once I am done with possible solutions, I will publish the diagrams on this forum for discussion.

    One lesson that I however learned so far is to me thorough when buying online.

  3. #13
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,677
    Thanks
    3,314
    Thanked 2,678 Times in 2,260 Posts
    Blog Entries
    12
    Quote Originally Posted by Derlyn View Post
    That's a VOV output. You cannot just bridge neutral to earth on that output.
    Not just a floating neutral?
    Or did you check the specs on the unit?

  4. #14
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,569
    Thanks
    110
    Thanked 149 Times in 141 Posts
    Quote Originally Posted by Dave A View Post
    Not just a floating neutral?
    Or did you check the specs on the unit?
    The specs on these types of inverters only give the live/neutral voltage output.

    I was probably a bit hasty with my VOV reply. Its just seldom that one measures a floating neutral scenario so close to exactly half the supply voltage. ( possible, but seldom )
    Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs.
    I was under the impression that the author had done this.

    Had he not, it will be interesting to know the outcome after doing so.

  5. #15
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,187
    Thanks
    59
    Thanked 102 Times in 97 Posts
    This is the way I understand the logic, right or wrong, I am sure someone will correct me.

    Genrators, UPS, inverters and the like are designed for a specific application, which is why they are class 11 devices, not orginally designed to be connected to fixed electrical installation.

    A class 11 devices doesnt have a floating neutral, it has 110 VAC on each leg, which reduces the voltage to make it a little safer for mobile use.

    A floating neutral is a floating neutral in a 3 phase supply which creates an extremely dangerous situation, in the past neutral condustors have been stolen in sub station because the thief has learnt that they will not get electricuted if they cut it.

    IF you are an electrician and been called out for a burning smell in a property, or burnt plug tops, ballasts and the like, you would have carried out tests and realised that the power had to be switched off asap, why because the voltage measured would in some cases be as high as 600-700 VAC

  6. #16
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,496
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by JackC View Post
    But I will try to make it as save as possible by introducing an ELU.
    An ELU will not work if you do not earth the inverter 'output Neutral', as there is no return path for the detection coil to operate.
    I suspect that with all these inverters, there is usually a small value capacitor connected between the inverter output and the 'Neutral' leg of the output plug.
    This capacitor cause the typical readings that you get with your multimeter when measuring the output of the inverter.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  7. #17
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,569
    Thanks
    110
    Thanked 149 Times in 141 Posts
    @ Justloaded. The way I understand it is that the earth leakage will work if the neutral and earth is not bridged on the output.

    If someone were to shock down to earth , then the difference in currents between the live and neutral will be detected by the earth leakage and it will trip, much the same as if one shocks down to earth from a double insulated appliance that is fed with live and neutral only, excluding an earth.

    However, should the output of the inverter be in a vov configuration, then the earth leakage wont trip.

    Correct me if I'm wrong.

  8. #18
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,496
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    @ Derlyn. The inverter shown by the OP does not have a VOV. They have a booster circuit multiplying the 12V Battery through a transformer to 230V AC out. So the battery and earth is effectively isolated by the transformer. If the Inverter Neutral output is not connected to earth before the ELU, the the ELU will not work. Of course the "Earth" connection is important, not only to the metal housing of the inverter, but also to the 'House' earth, as one would expect this to be a good earth point.

    I can not vouch for the VOV, in which the 'O' connection is earthed, if it would trigger the ELU. Theoretically it should.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  9. #19
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,569
    Thanks
    110
    Thanked 149 Times in 141 Posts
    Thank you, my brother, much appreciated. 👍👍

  10. #20
    Junior Member
    Join Date
    Jan 2023
    Location
    Pretoria
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts
    "Of course the correct way, as with a generator as well, is to connect a load to the output before taking voltage measurements. I use incandescent light bulbs"

    I done it with a small hair dryer as load, the voltages remain the same as tested previously. I also tested the current with a clamp meter both on live and neutral (basically the same 2.3 Amp) and when I include both neutral and live in the clamp meter I get a reading of 0.07 Amp. As explained by various forum members it seems like an inverter developed specifically for mobile use.

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Neutral earth bonding on backup systems.
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 145
    Last Post: 24-Mar-24, 04:37 PM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  4. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM