This is a monster, well at least for me.
It comes prewired, pre-everything you just have to hook it up, this is where my questions start.
There is a GEWISS AC in breaker 40A 2pole, a Hager 4pole 63A changeover, and an ACDC 2pole surge arrestor with a Lyn contactor for a bridge.
Questions:
Why is there is not an AC out breaker? Do I have to install one?
The stickers were covering the labels of the breakers. If you can't read the labels of a breaker you can't COC it.
Aluminum flex conduit with sharp ends houses the pv strings to the inverter. Not my problem, or is it, since it came from the factory like that?
The rest of the work was done pretty need.
How do you connect the ups to the mains since you can't just plug it in somewhere? Since you don't get 40 amp 1-phase socket.
Do you connect the UPS directly to a db somewhere on site with a 40Amp breaker and then to the earth leakage?
Or do you have a sub-db with two 2-pole breakers to which you connect the ups and then to the main db with 40Amp mains and earth leakage?
Or maybe two isolator switches you use to connect the ups too with a supply and return from the main db?
I would love to have a place close by where I can isolate the power for testing, disconnecting and isolating. How would you do it?
I have to COC it and refuse to do it. My main reasons are:
The AC out goes directly from the changeover to the earth leakage, relying all the way on the inverter for protection. Also, the only way to isolate the AC out is by switching off the changeover.
Also, the AC in comes from the prepaid via a changeover directly to the inverter, having no protection other than the breaker on the council side.
Any advice would be appreciated.