    Earth/neutral bond relay size

    This is a question many people are asking.

    I have been installing relay to suit the neutral conductor

    5 kva = a 25 amp relay

    8 KVA = 40 amp relay

    Do you really need a 20/25 amp relay/contactor for a 5 kva unit?

    or a 32/40 amp realy/contactor?

    IF you have a 4 mm neutral wire then you should have a 32 amp relay.

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    I think the question should rather be,
    Will the relay contacts survive/support a fault current to allow the circuit breakers to trip.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I agree with Justloadit
    Need to size according to max possible fault current which would be normally be around 1,5 times the nominal current for 10sec

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    So my relays are correctly rated

  5. #5
    New Member
    Join Date
    Aug 2023
    Location
    Pretoria
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    @Isetech

    Do you mind sharing which relay you are using? Also how you are wiring said relay?

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I use the din mount hager relays, yet to have one fail.

    Quote Originally Posted by McGuywer View Post
    @Isetech

    Do you mind sharing which relay you are using? Also how you are wiring said relay?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  7. #7
    Junior Member
    Join Date
    Aug 2016
    Location
    Cape Town
    Posts
    17
    Thanks
    0
    Thanked 1 Time in 1 Post
    Under no circumstance may you use an external relay or contactor to bond the neutral and earth

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @ Leonsparky. Most inverters have a dedicated output to energize an external relay for neutral earth bonding during islanding mode, so I do not agree with your statement above.
    In fact, it is the only way to do it - by making use of an external relay.

  9. #9
    Silver Member
    Join Date
    Mar 2008
    Posts
    373
    Thanks
    5
    Thanked 51 Times in 44 Posts
    Quote Originally Posted by Derlyn View Post
    @ Leonsparky. Most inverters have a dedicated output to energize an external relay for neutral earth bonding during islanding mode, so I do not agree with your statement above.
    In fact, it is the only way to do it - by making use of an external relay.
    This story has been going on for ages. The AIA inspector catagorically says it must perminantly be bonded. I figure if ever anything ever goes really wrong and I end up in court the guy opposite me is going to be the AIA guy. I understand implications of permenant bond and implications of relays (should it fail) but if the main man, the guy from the AIA says permanent - I do permanent.

    The ECA are a bit wishy washy on it(apparently I'm not reading it right) - depends on how you read the rules.

    Haven't picked up my new copy yet but hopefully there is some clarity.

    The basic argument is - if the relay fails will your earth leakage still operate.

  10. #10
    Junior Member
    Join Date
    Aug 2016
    Location
    Cape Town
    Posts
    17
    Thanks
    0
    Thanked 1 Time in 1 Post
    An external relay is probably the most unsafe thing ever. I have posted a very long argument in another thread but can't seem to find it.
    NRS chairman and I have done various test now too, we have given this info to the Working group, no changes as of yet but it will most probably say that no external contactor or relay/device may be used other than that of the manufacturer and supplied within a control panel such as the Sigenergy or Solaredge or Victron. Until then or anything else in SANS, permanent bond because that is what SANS says.

Similar Threads

  1. Neutral/earth bond for inverters
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 100
    Last Post: 14-Apr-23, 10:52 AM
  2. Size of Earth conductor
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 07-Jun-22, 01:36 PM
  3. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  4. [Question] Poor Neutral/Earth Bond - Stubborn Nuisance Trips
    By Ewaldvdh in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 23-Mar-22, 01:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •