    Neutral Earth - more info

    Hello

    So did a test yesterday, after Ians said he measures 9 Amps on a bridge wire (perm one)

    I was at a site where by I had a bridge and thought let me put a fuse in to test something before I do the contactor.

    So I put a 15A fuse in.

    So before fuse and at around mid day I measure 2.3A on the perm bridge, It then went to loadshedding and measure 0A.

    I then did the fuse wire and this morning I get a message of Earth leakage trips when power goes or comes back.

    I head back and see the 15A fuse has popped.

    So in essence when grid is on... Your perm bridge is the better path if the street PEN is shoddy.

    So do the contatcor.

    Next is to draw and figure out why that bridge which is after the inverter or load side of inverter creates a better N and E than the one at the Tx or kiosk...

    Sent from my CPH2197 using Tapatalk

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    To add, reason the bridge is there is I had a call from installer saying the Victron relay is giving a ground fault relay error.

    Long story short, switched off the relay and put in bridge wire then all sorted in the system worked and the ELU didnt trip.

    I thought great, now let's put in the contatcor. Then that is when I did the fuse test thing.

    So I think the Victron have that error not that there was a earth neutral issue (also it does not test for that in the new models ) but that it did pick up a voltage and that was the current using the earth's and Neutrals as return and higher earth current.

    Sent from my CPH2197 using Tapatalk

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,228
    Thanks
    60
    Thanked 103 Times in 98 Posts
    When I see this topic or the safe guidlines to installing lithium batteries etc, I just smile.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,228
    Thanks
    60
    Thanked 103 Times in 98 Posts

Similar Threads

  1. Sunsynk no earth, no dedicated neutral bar
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 10-Feb-23, 09:14 AM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •