    Hello to all.
    I need some advice from the people who know how the internal circuits work on the hybrid inverters. Mine is a 3KVA 24V with a built in charger and solar panel input (none currently connected).

    With the Eskom supply on, the socket outlets fed from the sub DB (inverter supplied) are working correctly. The earth leakage tester trips out the unit in the sub DB (Q3). However, if the Eskom supply fails (Q1 main DB off) and the circuit is then supplied from the battery / inverter then the earth leakage (Q3) does not trip.

    The EV with Eskom on is 0.15V and when the Eskom power is off and the sub DB is running on the inverter the EV is 45V.

    I have measured between the 'raw' neutral at the main DB and the neutrals at the changeover switch on position I and II. Pos I - virtually zero. Pos II - 45V.

    Click image for larger version. 

Name:	Screenshot 2023-02-18 083719.jpg 
Views:	574 
Size:	50.9 KB 
ID:	8703

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    You need to fit a relay/contactor to bridge neutral and earth on the output of the inverter when mains fails

    When mains comes back on the bridge between neutral and earth needs to disconnect

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    It looks like you are missing the neutral/earth bridge on the inverter output (UPS)


    Measured at the inverter UPS output in islanding mode (these are generally the readings you will see of the neutral/earth bridge is not fitted.)

    L-N = 230 VAC
    L-E =80 VAC
    N-E = 125 VAC

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    the "changeover" switch in the drawing is not a changeover switch, it is a bypass switch used to isolate the inverter in case you need to work on the inverter.

    I would modify the drawing and fit a double pole geyser type mcb for the bypass switch and a double pole geyser combo type ( I find it is way cheaper top use a double pole isolator) for the inverter input.

    The way your drawing is wired at the moment, would result in your bypass switch serving no purpose if the inverter is removed for what ever reason.

  5. #5
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by Isetech View Post
    the "changeover" switch in the drawing is not a changeover switch, it is a bypass switch used to isolate the inverter in case you need to work on the inverter.

    I would modify the drawing and fit a double pole geyser type mcb for the bypass switch and a double pole geyser combo type ( I find it is way cheaper top use a double pole isolator) for the inverter input.

    The way your drawing is wired at the moment, would result in your bypass switch serving no purpose if the inverter is removed for what ever reason.
    Should the inverter fail the switch can be moved to position I and the circuit will be fed from Eskom mains only.

  6. #6
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by GCE View Post
    You need to fit a relay/contactor to bridge neutral and earth on the output of the inverter when mains fails

    When mains comes back on the bridge between neutral and earth needs to disconnect
    Is there any reason why the inverter manufacturers don't include this in their circuitry? Even if the supply is not fed from TN-S then the software could be set to disable the internal relay.

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    How do you isolate and disconnect the inverter without interfering with the grid bypass?


    Quote Originally Posted by RegElec View Post
    Should the inverter fail the switch can be moved to position I and the circuit will be fed from Eskom mains only.

  8. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Some of the better quality inverter do have built in relays and/or terminals to control a relay.

    No SABS, no control.

    You must have an axpert type inverter. (meccer,RCT,MCE, etc etc) there are lots of rebranded units.

  9. #9
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by GCE View Post
    You need to fit a relay/contactor to bridge neutral and earth on the output of the inverter when mains fails

    When mains comes back on the bridge between neutral and earth needs to disconnect
    So something like this then:
    Click image for larger version. 

Name:	Screenshot 2023-02-18 110056.jpg 
Views:	548 
Size:	52.8 KB 
ID:	8704

  10. #10
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Your drawing is incorrect.

    Just a quick tip, if you decide to use a relay, makes sure the switch over from grid to islanding and back is instantaneous and relay functions at the same time.

    If there is a delay switching back to mains, make sure you link the relay coil to the contact or source that controls the switch over.

Page 1 of 2 12 LastLast

Similar Threads

  1. Inverter feed
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 14-Aug-22, 01:43 PM
  2. 3 KVA inverter
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 01-Apr-22, 04:39 PM
  3. Inverter and UPS
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 07-Oct-21, 01:20 PM
  4. 5 kva inverter
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 14-Feb-21, 10:34 AM
  5. [Question] Mr Power Inverter
    By Max123 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 14-Jul-18, 06:18 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •