    Just when you thought it couldnt get any worse

    Time to throw away your current clamp meter.


    https://www.youtube.com/watch?v=i6IN...hannel=Sunsynk

  2. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    A nice little test for all the smart people.

    The inverter is drawing 16 watts.

    The current clamp indicates 80 watts.

    Lets see some calculations.

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    By the way KW= KVA X PF

    5000 VA inverter with a 0.8 PF = 4000 watt inverter

    Some inverters claim they have a PF of 1, that means a 5000 VA (5 KVA) x 1 = 5000 watts (5 KW)



    This was a discussion had many years ago when LED became the next best thing since sliced bread.

    Some LED had a PF of 0.2. Install 2000 of them in a commercial building it could get interesting.

    Led lamps have improved since then, I do believe the PF factor has improved to at least 0.5 and better.

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Very keen to watch this later.

    I see on those small voltronkcs it gives Watts and VA... VA always more.

    Where this to me is interesting is that the battery needs to discharge all the power so the KVA. So using watts is not accurate.

    I see it draw 1000 watts, but actually it could be 1200 VA (depending on all the loads PF) so the battery then will not run to calculations

    Sent from my CPH2197 using Tapatalk

  5. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    The reason why ESKOM wants you to be close to unity in your load, as the generators have to generate amps as opposed to KVA.

    Another reason to understand that there is equipment out there which has a specification as "PFC" also known as power Factor Correction.
    This is done electronically, in which the electronics by doing boost switching, ensures that the same current is drawn from the supply all the way from the zero crossing to the peak of the cycle, and rectifying it into a DC, which is then fed into the equipment that consumes the energy.

    Effectively an inductive load such as a motor on a VSD drive now draws power from the grid with a unity power factor.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Similar Threads

  1. EVEN WORSE POWER PROBLEMS?
    By Phil Cooper in forum General Chat Forum
    Replies: 9
    Last Post: 22-Oct-15, 06:33 PM
  2. Injustice - getting better or worse?
    By Dave A in forum South African Politics Forum
    Replies: 4
    Last Post: 10-Feb-11, 09:42 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •