    Grounding and earthig of PV systems

    Grounding and earthing are two different concepts but interrelated.
    Bonding is to ensure that all the metal items are at the same potential to protect persons and animals.
    Earthing plates, which have small spikes on both sides, are a good idea between the panels and rails to avoid corrosion high resistance.
    The rails are bonded to the DC surge protection using 6mm yellow/green wire and then on to the DB earth bar.
    The inverter and battery casings are also bonded individually to the DB earth bar topreserve the integrity in the event of one item being removed.

    Adding to the importance of the panel earthing is that panels can be damaged and leak to the frame. Some inverters can detect this and cause an alarm.

    The NRS standard only allows one earth, namely the TN-S earthing system of the Supply authority.
    Additional earth spikes are not permitted due to the potential difference of a nearby strike. This creates a current flow through the bonding causing possible damage.
    GCE covers this well in another reply.

  2. #22
    New Member
    Join Date
    Nov 2023
    Location
    In your head
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post
    The panels we use, are class II rated so they should not be leaking power to the frame. The solar cabling is also double insulated, so unless someone is going out of their way to damage the equipment, you shouldn't experience leakage problems.


    Quote Originally Posted by StepupEnergy View Post
    Adding to the importance of the panel earthing is that panels can be damaged and leak to the frame. Some inverters can detect this and cause an alarm.

  3. #23
    New Member
    Join Date
    Nov 2023
    Location
    In your head
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post
    I am yet to see an earth mat installed for a solar installation. That is why specialized tasks should be carried out by people who are specialists in that field, not by a bunch of clowns who think randomly knocking in a bunch of earth spikes around a property is going to cut it.

    Quote Originally Posted by GCE View Post
    The earthing on for instance a tower with an earth mat in the ground will take the ionization that forms in the air down to earth using the earth mat to dissipate the voltage
    At the point in time the potential difference in the earth will lift closest to the earth mat and become less further away - Animals legs are 1,5m apart and therefore the potential difference can increase between the legs briefly and sufficiently to electrocute them - The increase in potential difference is dependent on the proximity on the lightening
    Is the reason you should shuffle if walking outside in a thunderstorm and the reason why the 2 guys carrying an extension ladder of 5m in a thunderstorm took a big hit - It was not a direct strike but just that they were in close enough proximity of where the lightening happened to hit the ground and the distance between them joined with an aluminum ladder increased potential difference across them .

    The potential difference of the ground depending on the size of the strike can be in a conical effect over a distance of 2KM - the attached oic gives an idea

    Attachment 8692

  4. #24
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    40
    Thanks
    43
    Thanked 0 Times in 0 Posts
    It makes sense Shadyshaun but what if the authorities requires an earth spike?
    So bonding the solar panels to your DB earth,- in an event of thunder would fry the earth wires?

  5. #25
    New Member
    Join Date
    Nov 2023
    Location
    In your head
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post
    The site assessment and design will determine the specifics. Electricians are not design engineers, nor are they lightning specialists and therefore should not be offering solutions, which do not fall within their scope of expertise. It would appear (reading comments on social media) that many electricians feel that one size fits all and every application is exactly the same, you will even be rewarded with certification once you have completed a certain number of installations.

    If the design criteria specifies an earth spike, it should be installed.

    Would an earth wire fry, it would depend on the intensity of the strike. Without testing the resistance of the earth wire, you would never know the impact of the strike. It may appear to be ok, however in some cases the wire could reach such extreme temperatures that it would render the wire pretty useless.

    If you have been in the electrical industry for a while, you would have noticed wires which are no longer "shiny bright copper" , they are not as flexible and turn a blue/black colour, they should be replaced.




    Quote Originally Posted by Gene View Post
    It makes sense Shadyshaun but what if the authorities requires an earth spike?
    So bonding the solar panels to your DB earth,- in an event of thunder would fry the earth wires?

  6. Thanks given for this post:

    Gene (24-Dec-23)

  7. #26
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Shadyshaun View Post
    The panels we use, are class II rated so they should not be leaking power to the frame. The solar cabling is also double insulated, so unless someone is going out of their way to damage the equipment, you shouldn't experience leakage problems.
    SANS 10142-1 requires that the frames shall be bonded to earth - The reason for bonding is in case of a fault like somebody intentionally/unintentionally damaging the equipment


    Extract from SANS 10142-1
    6.12.3.3 Metallic frames and metallic enclosures of electrical equipment shall
    be made electrically continuous.


    6.13.2.4 Roofs, gutters, down pipes and waste pipes
    If a building is connected to an electricity supply, the roof(s), gutter(s), down
    pipe(s) and waste pipe(s) shall be bonded and earthed and the resistance of
    the earth continuity path shall not exceed 0,2 Ω, unless
    a) the supply voltage does not exceed 50 V,
    b) the supply uses an underground service connection,
    c) the roof is made of, or covered with, non-conductive material,
    d) the gutter(s), down pipe(s) and waste pipe(s) are of non-conductive
    material, or
    e) the gutter(s) and down pipe(s) are attached to a metal roof that is covered
    with non-conductive material.

  8. #27
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Shadyshaun View Post
    T
    If you have been in the electrical industry for a while, you would have noticed wires which are no longer "shiny bright copper" , they are not as flexible and turn a blue/black colour, they should be replaced.
    Where the wires are Blue/Black in color it would mean that excessive current has been drawn through the copper and you would need to see why before just replacing.

    It is one of the reasons that running an earth wire all the way down to a Borehole pump is no longer needed as the earth to the pump ended up being the best earth around and taking excess current down to the "earth Rod hanging in water 100m down" - You would always find a borehole earth wire went blue/black in color

  9. #28
    New Member
    Join Date
    Nov 2023
    Location
    In your head
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post
    You seem to be a smart person with a fair amount of insight into he SANs regulations, do you know why this section of the code was created many many years ago? I doubt it has anything to do with class II double insulated solar panels.

    The next question I would ask, if the frame poses a risk, why dont the panels have a simple certified method for bonding, supplied or attached to the panel, similar to the MC4 connector?

    Just imagine if light fittings where supplied with a hole and a symbol, do you think electricians would bother connecting an earth wire. The only reason some electricians consider connecting the cover of certain lights to earth, is because there a spade connector provided.




    Quote Originally Posted by GCE View Post

    6.13.2.4 Roofs, gutters, down pipes and waste pipes
    If a building is connected to an electricity supply, the roof(s), gutter(s), down
    pipe(s) and waste pipe(s) shall be bonded and earthed and the resistance of
    the earth continuity path shall not exceed 0,2 Ω, unless
    a) the supply voltage does not exceed 50 V,
    b) the supply uses an underground service connection,
    c) the roof is made of, or covered with, non-conductive material,
    d) the gutter(s), down pipe(s) and waste pipe(s) are of non-conductive
    material, or
    e) the gutter(s) and down pipe(s) are attached to a metal roof that is covered
    with non-conductive material.

  10. #29
    New Member
    Join Date
    Nov 2023
    Location
    In your head
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post
    Generally, we would scan the electrical installation with a thermal camera, use a clamp meter to measure the current, check the overload protection rating, review the data and create a report with recommendations.

    There are many factors to be taken into consideration, loose connection, bad contacts in the switch gear, unbalanced loads just to mention a few. We have also found that in some case it is just due to the high demand over a long period of time.


    Quote Originally Posted by GCE View Post
    Where the wires are Blue/Black in color it would mean that excessive current has been drawn through the copper and you would need to see why before just replacing.

  11. #30
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Shadyshaun View Post
    You seem to be a smart person with a fair amount of insight into he SANs regulations, do you know why this section of the code was created many many years ago? I doubt it has anything to do with class II double insulated solar panels.

    The next question I would ask, if the frame poses a risk, why dont the panels have a simple certified method for bonding, supplied or attached to the panel, similar to the MC4 connector?

    Just imagine if light fittings where supplied with a hole and a symbol, do you think electricians would bother connecting an earth wire. The only reason some electricians consider connecting the cover of certain lights to earth, is because there a spade connector provided.
    Bonding of external parts has also been part of the code and PV panels have also been around for years and if you want to have more relevant codes specific to PV panels then 7.12.7.6 refers you to that particular clause ( extract pasted below )

    Clause 6.12.3.1 e - clearly states earthing terminal of all permanently connected electrical equipment - The PV panels have a earth point referred to as grounding point - check your panel spec and warranty document - The manufacturers of structures have provided simplified bonding arrangements for a reason

    Clause 5.1 clearly states that you need to comply with manufacturers requirements .

    Clause 7.15.2 of SANS 10142-1 also requires bonding of wireways etc in DC systems and under 7.12 you are referred to 7.15

    Then if you are still trying to convince yourself that SANS 10142-1 is not relevant to PV panels then clause 7.12.7.1 from SANS 10142-1 refers you to SANS 60364-7-712 which has numerous references to earth including the earthing of structures and uses the word " Shall" - extract pasted below


    SANS 10142-1
    7.12.7.6 If applicable, all exposed conductive parts may require earthing as
    prescribed in 6.12.3.


    5 Fundamental requirements
    5.1 General
    All commodities in an electrical installation shall be installed in accordance
    with the requirements in this part of SANS 10142 and with the manufacturer's
    instructions,
    where applicable.
    NOTE 1 This clause contains the general safety principles applicable to electrical
    installations.
    NOTE 2 The manufacturer's instructions may contain more stringent requirements.


    Extract from SANS 60364-7-712
    712.542.103 Bonding of PV metal structures
    Where such bonding is necessary (e.g. to facilitate the correct operation of the array
    insulation resistance detection referred to in 712.531.3.101.1), the metallic structures
    supporting the PV modules (including metallic cable trays) shall be bonded.

    Such bonding may be necessary, for example, where a transformerless PCE induces an
    electrostatic charge.
    The bonding conductor shall be connected to any suitable PE terminal.
    Where these metal structures are of aluminium, appropriate connection devices shall be used.
    The bonding conductors (insulated or bare) shall have a minimum cross section of 4 mm2
    copper or equivalent.
    PV array bonding conductors shall be run as close to the positive and negative PV array and
    or sub-array conductors as possible to reduce induced voltages due to lightning. See also
    712.521.103.

Page 3 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. Solar power panels
    By reggy in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 28-Feb-23, 10:25 PM
  2. Installing solar panels
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 52
    Last Post: 07-Jan-23, 10:52 PM
  3. Lightning 6.7.7 and surge protection 6.7.6
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 13-Sep-22, 05:40 PM
  4. Lightning and surge protection insurance
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 25-Nov-21, 03:34 PM
  5. Lightning protection vs surge protection
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 28-Feb-20, 08:02 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •