6.13.2.4 Roofs, gutters, down pipes and waste pipes
If a building is connected to an electricity supply, the roof(s), gutter(s), down
pipe(s) and waste pipe(s) shall be bonded and earthed and the resistance of
the earth continuity path shall not exceed 0,2 Ω, unless
a) the supply voltage does not exceed 50 V,
b) the supply uses an underground service connection,
c) the roof is made of, or covered with, non-conductive material,
d) the gutter(s), down pipe(s) and waste pipe(s) are of non-conductive
material, or
e) the gutter(s) and down pipe(s) are attached to a metal roof that is covered
with non-conductive material.