    Quote Originally Posted by Isetech View Post
    At least this clears up the original question, you can use split conduit to for added protection.

    It also clears up the talk about the double insulated cables in the same wireway. To add to the confusion, what about the single insulated 6 mmsq earth wire installed in the same conduit, I see most installers have a single insulated earth wire inside the same wireway ?
    You need to understand the logic behind the regulations - The reason for running positive and negative in th esame wireway as earth is for in case of arching the neg or live can short to earth and the inverter will detect the fault and switch off

    Wire ways are still under consideration under SANS60364-7-712 - SANS 10142-1 is clear on using a wireway

    712.527 Selection and erection of wiring systems to minimize spread of fire
    Under consideration.

  2. #12
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,271
    Thanks
    34
    Thanked 308 Times in 260 Posts
    The unfortunate part with the way people read regulations is to suit themselves - muddy the water and confuse everyone so that all an sundry then say there are no regulations for solar installs.

    Solar install is the same as normal wiring besides there being one or two other points which are clarified under DC .

    We been installing DC systems from early days with motors , UPS battery systems etc

  3. #13
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,271
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Quote Originally Posted by Douggie View Post
    Question: Using the black split conduit. Is it compliant in SA to use it everywhere? High Rise buildings etc.?
    Further to my previous post on split conduit and having a think on it

    SANS10142-1 clause 6.5.1.1 i) would answer that one as well


    6.5.1.1
    i) no part of the wireway shall be flattened, split or damaged;

  4. #14
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,079
    Thanks
    56
    Thanked 98 Times in 94 Posts
    From what I understand, you have to have protection where the solar wire and earth exits the roof, which means you need some form of protection, what wireway do you use?

    Why dont we install twin+E in a wireway, because it is double insulated?

    I am trying to wrap my head around the logic, its been a hectic 2 weeks of challenges with high end NVR's and IP cameras, software, firmware, another 5 hours in meetings today trying to resolve challenges and slow networks.





    Quote Originally Posted by GCE View Post
    Further to my previous post on split conduit and having a think on it

    SANS10142-1 clause 6.5.1.1 i) would answer that one as well


    6.5.1.1
    i) no part of the wireway shall be flattened, split or damaged;
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  5. #15
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,271
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Quote Originally Posted by Isetech View Post
    From what I understand, you have to have protection where the solar wire and earth exits the roof, which means you need some form of protection, what wireway do you use?

    .
    There are manufactured units designed for different roof structure exits - We prefer taking the conduit over the edge of the roof with a drip loop into a junction box with a breather at the bottom before entering the roof space .
    It stops any water ingress and damage to undertile waterproofing .

  6. #16
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,271
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Quote Originally Posted by Isetech View Post

    Why dont we install twin+E in a wireway, because it is double insulated?

    .
    Maybe because the design and manufacturing process for the " sheath " is different to street insulation ?

  7. #17
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,079
    Thanks
    56
    Thanked 98 Times in 94 Posts
    Thats not a bad idea because you could fit your DC isolator on the side of the building

    Quote Originally Posted by GCE View Post
    There are manufactured units designed for different roof structure exits - We prefer taking the conduit over the edge of the roof with a drip loop into a junction box with a breather at the bottom before entering the roof space .
    It stops any water ingress and damage to undertile waterproofing .
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Neutral split
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 19-Nov-22, 06:12 PM
  2. Metal conduit requirement for DC PV Wires
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 28-Sep-22, 02:40 PM
  3. [Question] Equity split
    By Nickolai Naydenov in forum Entrepreneurship and Business Management Forum
    Replies: 5
    Last Post: 07-Aug-13, 09:36 PM
  4. The value of split-testing
    By Norri in forum Marketing Forum
    Replies: 5
    Last Post: 22-Jun-12, 02:18 PM
  5. [Question] What happens when 2 CC directors split up?
    By Dave D in forum General Business Forum
    Replies: 10
    Last Post: 24-May-12, 04:07 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •