    Leakage on earth wire

    Hi All,

    I'm trying to understand a situation we have in our home and would appreciate any feedback.
    We started noticing that while bathing, if we touched the tap we would get a small electric shock. I measured 5V AC between the tap and earth, I don't know the amperage.
    I then went around measuring other taps, and it seemed mainly on the hot water tap.

    So we called out a sparky who couldn't make sense of it either. The earthing straps on the geyser were all there and everything looked proper he said. At the geyser he was measuring 12V.
    Eventually he said the problem was solved and that he had 'separated some wires'. So I'm guessing that relates to induction current? (He also redid our DB and installed type 1 & 2 surge protectors while he was at it)

    Needless to say the problem is back. I went to check the garage DB and noticed a tingle while touching the DB box. There I measured 10V from the earth wire to the actual ground.
    My wife swears the problem seems to happen after it has been raining. Which could mean water getting into something and causing a short, but not enough to trip a breaker?
    I really don't know where this leakage is coming from, could it even be coming into the house from Eskom's side?

    Cheers,
    Robert

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    The chances are about 95% that there's a high neutral impedance. The fault is probably outside on the transmission line between your house and the sub station.

    Find out from your neighbours if they are also experiencing a tingle from their taps. If so, phone the supplier and report it. The neutral might have been stolen somewhere.

  3. #3
    New Member
    Join Date
    Nov 2022
    Location
    Kempton Park
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Derlyn View Post
    The chances are about 95% that there's a high neutral impedance. The fault is probably outside on the transmission line between your house and the sub station.

    Find out from your neighbours if they are also experiencing a tingle from their taps. If so, phone the supplier and report it. The neutral might have been stolen somewhere.
    Thanks for the response. I tested the taps last night will all circuit breakers off. Still getting tingles from the tap.
    I've asked the neighborhood if any one else is experiencing this. Hopefully it's not something between our house and the suppliers box.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    If your electrician did a neutral impedance test when you called him, he would have known immediately whether the problem is on your installation or not.

    When called out for tingling taps, that's the first test that any electrician worth his salt should carry out.

    From experience, we have found that tingling taps is very seldom caused by a fault on the load side of the main breaker. Almost always a bad neutral connection on the supply.

    If you have an overhead supply, the problem can be in the roofbox on your house in which case it will be your responsibility to have it repaired. Anywhere before the roofbox is the supplier's responsibility, be it municipal or eskom.

    Good luck.

  5. Thanks given for this post:

    Schuits (14-Nov-22)

  6. #5
    New Member
    Join Date
    Nov 2022
    Location
    Kempton Park
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    With 20 years or more experience I'm sure he knew exactly what he was doing.
    But telling me to call my power supplier wouldn't have earned him any money, so he found something else to do and made a buck anyway.

    In future I think I'll take by business elsewhere.

    No roofbox here, everything comes from underground and connects to a small box on the outside wall.



    Quote Originally Posted by Derlyn View Post
    If your electrician did a neutral impedance test when you called him, he would have known immediately whether the problem is on your installation or not.

    When called out for tingling taps, that's the first test that any electrician worth his salt should carry out.

    From experience, we have found that tingling taps is very seldom caused by a fault on the load side of the main breaker. Almost always a bad neutral connection on the supply.

    If you have an overhead supply, the problem can be in the roofbox on your house in which case it will be your responsibility to have it repaired. Anywhere before the roofbox is the supplier's responsibility, be it municipal or eskom.

    Good luck.

  7. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I wouldn't go pointing fingers at a person if they haven't been given the opportunity to read and respond to the post, this is the problem with social media.


    Quote Originally Posted by Schuits View Post
    With 20 years or more experience I'm sure he knew exactly what he was doing.
    But telling me to call my power supplier wouldn't have earned him any money, so he found something else to do and made a buck anyway.

    In future I think I'll take by business elsewhere.

    No roofbox here, everything comes from underground and connects to a small box on the outside wall.

  8. #7
    New Member
    Join Date
    Nov 2022
    Location
    Kempton Park
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    I agree and sincerely apologize. As someone who is ignorant of this topic I have no place judging him.

  9. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    One easy way that might help focus your search for this fault is try switching the geyser off on the circuit breaker in the DB before you get in the bath. If the tingling problem disappears it would point toward a geyser fault or a lack of bonding issue on the pipework maybe.
    _______________________________________________

    _______________________________________________

  10. #9
    New Member
    Join Date
    Nov 2022
    Location
    Kempton Park
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by AndyD View Post
    One easy way that might help focus your search for this fault is try switching the geyser off on the circuit breaker in the DB before you get in the bath. If the tingling problem disappears it would point toward a geyser fault or a lack of bonding issue on the pipework maybe.
    Ye I did that. With all circuit breakers off the issue is still there.
    The sparky offered to come install 3 earthing rods and remove the suppliers earth connection. I asked him just to hang on a bit to see if I can get the supplier out to fix the issue.

  11. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    If there's a supply neutral issue, then believe it or not, the better your earthing, the more pronounced that tingling is gonna get, believe it or not.

    A neutral fault on the supply, cannot be fixed on your installation.

Page 1 of 2 12 LastLast

Similar Threads

  1. Using the earth wire of the twin+E as alive conductor
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 26-Jun-22, 04:58 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. Why would you install MCB for an Earth wire
    By swordfish in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 27-Sep-21, 11:39 AM
  4. Earth leakage
    By Electrix in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 09:10 PM
  5. No earth wire!
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 02-Jan-16, 08:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •