    Coc question

    We do a fair bit of coc and never pretend to know it all. We have experienced electricians doing it for mostly all over 10 years. We one of the biggest eca registered in the area . We sometimes get into fights with the pure compliance companies who in some way in my view are too technical for context of sa . Make sure it’s safe but charging 30 k for niggly stuff like example cracked conduit in roof is in nobody’s interest . So my question . They say the neutral bar must be accessible . Any body know of such a law in the sans code. The db is very small and we issued a coc but never did the original board .

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I would think they are using 5.3.8 to make that statement bearing in mind that under D/Boards it refers to 5.3.8 and under 5.3.8 it forces you to go look at 6.6.1.9 - Directly below that is 6.6.1.11 which is self explanatory.
    They only issue may be the interpreting of " easily"



    5.3.8 Positioning and accessibility of electrical equipment
    Electrical equipment shall be so positioned that
    a) it does not impair the functioning or safety of other equipment,
    b) it is readily accessible for installation, replacement, operation, testing,
    inspection, maintenance, and repair (see 6.6.1.9 and 6.9.4 for the main
    switch). All parts of the installation shall be accessible without the need to
    enter any adjoining premises (for example, in an apartment building),
    NOTE Common areas (such as passages and entrance halls) are not regarded as
    adjoining areas.
    c) there is easy access to its location,
    d) it is not likely to be physically damaged,
    e) dust or moisture is not likely to accumulate on live or other parts and cause
    flashover, and
    f) where the distribution board is concealed by a cupboard or other covering,
    the notice for live electrical apparatus referred to in annex N shall be in a
    conspicuous place indicating the position of the distribution board

    6.6.1.9 Distribution boards shall be so positioned and arranged as to ensure
    safe operation and maintenance (see 5.3.8).
    6.6.1.11 A distribution board and the equipment mounted in or on it shall be
    so positioned and arranged that any conductor can easily be disconnected
    from the terminals.

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This would fail 80 % of installation in our part of town.

    Quote Originally Posted by Firepool View Post
    We do a fair bit of coc and never pretend to know it all. We have experienced electricians doing it for mostly all over 10 years. We one of the biggest eca registered in the area . We sometimes get into fights with the pure compliance companies who in some way in my view are too technical for context of sa . Make sure it’s safe but charging 30 k for niggly stuff like example cracked conduit in roof is in nobody’s interest . So my question . They say the neutral bar must be accessible . Any body know of such a law in the sans code. The db is very small and we issued a coc but never did the original board .

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I was asked to do a check on a property bought by one of my customers, I pointed out that most of the light switches and socket outlets were damaged (cracked). I was told , so long as the live electrical equipment cannot be touched with a standard test finger, it didn't have to be replaced. It is a cosmetic issue not a non compliant issues.

    We go back to the same thing I say every time, dont sign the transfer papers until you are happy with electrical installation.

  5. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Almost every single DB for domestic you can not access the N bar let alone the Earth bar. Even in installs of 30 years ago. The DBs are poor design almost all of the time.

    Need to mount 3 DBs, left the earth, middle the breakers and right the neutral bars...

    Sent from my CPH2197 using Tapatalk

  6. #6
    Email problem
    Join Date
    Sep 2021
    Location
    cape town
    Posts
    46
    Thanks
    0
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Dylboy View Post
    Almost every single DB for domestic you can not access the N bar let alone the Earth bar. Even in installs of 30 years ago. The DBs are poor design almost all of the time.

    Need to mount 3 DBs, left the earth, middle the breakers and right the neutral bars...

    Sent from my CPH2197 using Tapatalk
    Thank you .Exactly what we saying. There is a safe house and then there is applying the law but will never get the job.If you did the board like that you maybe have to answer but sign it off and you come up with that fault and what do you think the seller will say?Will say you fishing for work and then loose trust in your reputation.We wonder why the pure compliance companies have a bad name.

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Wait till you have to work on a floor standing DB with bussbars at the back, all I am going to say is eeeesih. I can tell you of some really silly days trying to hook the neutral current clamp on a live 3000 amp bussbar, which is normally right at the back, I stopped doing it, just too risky .

    DB's should be wide enough to mount the earth and neutral bars on the left and right of the panel.



    Quote Originally Posted by Dylboy View Post
    Almost every single DB for domestic you can not access the N bar let alone the Earth bar. Even in installs of 30 years ago. The DBs are poor design almost all of the time.

    Need to mount 3 DBs, left the earth, middle the breakers and right the neutral bars...

    Sent from my CPH2197 using Tapatalk

Similar Threads

  1. COC question
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jul-19, 10:11 AM
  2. [Question] Question about NPO's and NPC's
    By jilli13 in forum Accounting Forum
    Replies: 0
    Last Post: 01-Sep-16, 08:04 AM
  3. Question
    By Clever in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 04-Aug-16, 12:53 PM
  4. November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 10