  1. #141
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    There was a crowd that sat around a table and had the discussion that is how this article came about
    https://ecasa.co.za/technical/neutra...ing-clarified/

    Same way that there was a +/-6hr zoom meeting on Friday last week to get various manufacturers and others around a table for discussion over batteries with the view of putting out some sort of guidance which may still take awhile

  2. Thanks given for this post:

    Derlyn (19-Mar-24)

  3. #142
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,057
    Thanks
    56
    Thanked 97 Times in 93 Posts
    Either way it cant be that dangerous, otherwise the sale of these units would be halted, warning labels would be required exposing the dangers and there would be court cases.

    Bottom line, just do what you think is right because at the end of the day it is not up to the electrician or installer to make the regulations.

    Make sure whichever method you use, have the support of that group.

    Has anyone done any tests with a meter ?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  4. #143
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Only thing I have seen, is I had a perm neutral earth bond on the output of the inverter, I this time as a test put and inline 15Amp fuse in that perm bridge.

    Went back the next day and that fuse had popped.... When I measured current at that time I was getting 9Amps when the grid was available, when the inverter went into island mode I had 0amps on the perm bond...

    Sent from my CPH2197 using Tapatalk

  5. #144
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,490
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Dylboy View Post
    Only thing I have seen, is I had a perm neutral earth bond on the output of the inverter, I this time as a test put and inline 15Amp fuse in that perm bridge.

    Went back the next day and that fuse had popped.... When I measured current at that time I was getting 9Amps when the grid was available, when the inverter went into island mode I had 0amps on the perm bond...

    Sent from my CPH2197 using Tapatalk
    There should be no permanent Neutral/Earth bond on the output of the inverter if in Hybrid mode, or pass through mode, as the incoming supply would have this connection done at the transformer point.
    Only when the inverter changes to Islanding mode should the Earth/Neutral bond take place, as the inverter now becomes the supply source, and for proper ELU operation, the Earth/Neutral bond now takes over.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #145
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Yes 100%, it was an install of someone else which had tripping issues and saw the perm neutral earth bond in which I did some tests on, i did then add a contactor to make and break.

    Still was an interesting test and it came about a post from Isetech awhile back when he measured current on the earth so thought it would be a good test, it was quite awhile ago.

    Sent from my CPH2197 using Tapatalk

  7. #146
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by GCE View Post
    I would hazard a guess and say you are going to be back there for a mains incoming neutral fault - Could be that there is a loose connection coming into the property and that every now and then it utilizes the inverter neutral due to the bonding
    @ GCE. You are a foretune teller supreme.

    Was called back on Friday for no mains power.
    Main breaker faulty. ( Replaced )
    After carefull inspection I noticed the telltale brownish burn mark on the neutral side of breaker.

    I can only assume that the breaker was on it's way out and that there was a high impedance across the neutral contact inside.


    Click image for larger version. 

Name:	20240322_091837.jpg 
Views:	33 
Size:	44.2 KB 
ID:	8901

Page 15 of 15 FirstFirst ... 5131415

Similar Threads

  1. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  2. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  3. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM
  4. Separation of AC and DC wiring in backup systems
    By ians in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 01-Dec-21, 07:41 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •