    Electic fence interfer with led fitting

    I got a client who asked me to install LED back up fittings at their complex. I installed the fittings below the electric fence cable which runs in a pvc conduit pipe. When the mains power is on everything works as it should but as soon as there is load shedding and the lights must come on at 30% of its brightness the lights is starting to flicker when the fence is pulsing. Any idea what I can do to prevent it from happening?

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Electric fences do give off inductance or what ever it's called. So it's sending voltage through the airgap and the cables are picking up the voltage.

    I am not sure how to fix it perhaps use shielded cable or braided cable to feed the LED and perhaps earth the braided sheath.

    Sent from my CPH2197 using Tapatalk

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Check your earth - have had it when a fence shorts down to earth and it brings LED on - Earth to the LED was a bit shitty and picking up the elevated voltage on the fence earth

  4. #4
    New Member
    Join Date
    Oct 2022
    Location
    Port Elizabeth
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Check your earth - have had it when a fence shorts down to earth and it brings LED on - Earth to the LED was a bit shitty and picking up the elevated voltage on the fence earth
    Thanks but the fitting and the led casings are all plastic so there is no place to connect the earth. Are you saying that I need to connect the one end of the supply cable earth feeding the light to the main earth of the house?

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Ian's electrical View Post
    Thanks but the fitting and the led casings are all plastic so there is no place to connect the earth. Are you saying that I need to connect the one end of the supply cable earth feeding the light to the main earth of the house?
    SANS10142-1 says you must

Similar Threads

  1. [Question] Neighbors' Electric Fence Bleeding into my fence
    By willemma in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 10-May-21, 07:37 PM
  2. Marketing of new patented electrical fitting
    By Richard S in forum General Business Forum
    Replies: 8
    Last Post: 17-Apr-16, 10:39 PM
  3. 12V fitting with 220V lamps
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 14-Feb-14, 01:59 PM
  4. freezer room light fitting
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 16-Jan-13, 09:21 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •