I have become involved in the upgrade of very old industrial machines in a mini factory. Part of the upgrade plan is to move from the ancient analogue control system to PLC control with VFDs controlling stepper motors.
Electrical supply is three phase to each machine and then at measured 415VAC with a total current requirement of 16A-23A depending on which electrical motors are running.
Inspecting the current installation there are C-curve circuit breakers in the main DB protecting the too small sized cabtyre cable to each machine. No neutral is supplied to any machine.
Currently isolation and overload protection at each machine is provided by a rotary 3P isolation switch and three bottle fuses (one per phase). Nothing more.
Each machine is managed by an operator which is in constant contact with the metal parts of the machine due to the operation requirements. Add to this a leaking roof with noticed puddles of rainwater where the operator is standing ... and yes no bonding of the machine ...
Now the fun part starts ...
My common sense tells me that with the upgrade each machine needs to be supplied with a MCB and a RCCB or RCBO to protect the operator and the new PLC system. I know the SANS regulations requirements for RCD protection on fixed machines have been discussed numerous times and it boils down to no stipulated RCD requirement is found for fixed industrial machines in the SANS 10142-1 document.
As this installation has numerous squirrel cage motors per machine, all the breakers leading to the machine and in the control cabinet at the machine, in my opinion, needs to be D-curve and not C-curve. Secondly the RCCB finds VFDs downstream of it, so this needs to be Type B.
The cost of such 4P circuit breakers and RCCB is rather on the heavy side (if you can currently find such in SA) and the customer is not willing to spend such funds. You know the saying: "It has been working fine like this for the past 40 years". Now add in the comments of the MIA electrician.
I would love to hear your comments regarding the above. Especially pertaining to the RCCB or RCBO units.
Now we also need to add the requirements of the OSHA Electrical Machinery Regulations :-)