So I need to quote to fix up someone else garden lighting and I have a few questions if that's ok.
So to start the previous oke ran Norsk cable to all the uplights in the garden but didn't bury them deep at all... Like most of it is sticking out...
So my questions are:
Do I quote to re do it all with Steel wire armoured cable and bury it as deep as I can and put them on Earth Leakage. (It's a rocky area so I can't bury too deep)
Or
Do I use 20mm PVC conduit over the Norsk and then bury where I can and then put them on earth leakage as well.
As we know PVC gets broken after a few years though.
I am Inclined to do the SWA but I would like some feedback please. To terminate and run that is a huge pain haha.
My old boss made us use Norsk and call it a day but I want to do things better where I can.
Norsk cable as far as I know is not mechanical protection but is it sheathed (I think so as it has that metallic layer)
6.4.4 Buried cables
6.4.4.1 Unarmoured cables may be buried if they are insulated and sheathed.
6.4.4.2 If unarmoured insulated cables are buried at a depth of
a) less than 0,5 m, they shall be enclosed in conduit or otherwise
mechanically protected (for example, in the case of paving or concrete)
(see also 6.5), or protected by an earth leakage protection device with a
rated earth leakage tripping current (rated residual current) IΔn not
exceeding 30 mA, or