    I'm going to put what I think after each one - see what everytome else says

    Silly petty things like

    exposed wires between the terminal block, - Fail

    earthing downlights, - if metal and not earthed - fail - us SANS approved GU10 lamp holder (with earth)- don't like them but can't fail them

    exposed metal light fittings higher than 2.4 m, - fail

    cracked switches and socket outlet covers, - fail - not suitable for use

    DB's behind the fridge, - grey area - you can't stop people putting fridge over their DB - was the fridg ethere when you tested - note in commenct section

    or above the stove, - fail

    or in cupboard, - in a domestic - fine as the owner knows where to isolate if a problem - I'll lable the cupboard during CoC

    Cabtyre feeding circuits, - apparently its ok now according the new reg - haven't had to deal with it yet so haven't looked it up

    Rip cord used for security lighting from a plug top, - fail

    Transformers feeding gates motors from the garage 50 m away, - not sure i get that one?

    intercom and power cables in the same wireway, - technically, a fail

    roof spaces which look like an alarm installer wired up everything, - usually a fail after some scratching around

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,060
    Thanks
    56
    Thanked 98 Times in 94 Posts
    For the record, cracked switches and plugs is not a fail, as I learnt he other day doing a COC audit. So long as you cant touch exposed wires with the standard test finger it is a pass if the cover is cracked.

    Just anotehr reason you wan the installation checked before you sign the transfer papers. Once you sign, you pay to replace the cracked covers or sockets and switches.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Electrical coc for sub db
    By Courtesy00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 30-Dec-21, 11:16 AM
  2. [Question] Electrical assessor
    By Lindley in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 28-Feb-19, 11:33 AM
  3. [Question] DIY electrical
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 05-Jun-11, 10:49 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •