    Question DB Surge protector installation SASP-15KA

    I recently saw SASP-15KA in the ACDC catalogue and for R140 it's cheap insurance.
    https://a365.acdc.co.za/Images/spec/...0SASP-15kA.pdf

    I see it has a rating of 15kA and 275V and uses MOV's (which arrest surges by simply shorting the supply once the voltage goes above the threshold)

    It doesn't say how it should be installed though.
    Does SANS specify where it should be installed?
    I would imagine it should be installed after the mains isolator. So the neutral output of the mains isolator connects to the bottom of SASP-15KA, and the live output of the mains isolator connects to the top of SASP-15KA ?

  2. #2
    Full Member
    Join Date
    Sep 2022
    Location
    Cape Town
    Posts
    33
    Thanks
    8
    Thanked 0 Times in 0 Posts
    Using a wire gauge that can carry more than 63A, given a 63A Mains Isolator.

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by LightsOn View Post
    Using a wire gauge that can carry more than 63A, given a 63A Mains Isolator.
    An Isolator gives no protection

  4. Thanks given for this post:

    LightsOn (23-Sep-22)

  5. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    On page 302 of SANS 10142-1-(3.01) has a diagram with location of the overload protection device and how to wire an SPD into a single phase system.

  6. Thanks given for this post:

    LightsOn (23-Sep-22)

  7. #5
    Full Member
    Join Date
    Sep 2022
    Location
    Cape Town
    Posts
    33
    Thanks
    8
    Thanked 0 Times in 0 Posts
    Thank you very much for your replies! Most helpful

  8. #6
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    131
    Thanks
    60
    Thanked 10 Times in 9 Posts
    I install after main switch and before earth leakage. Shortest possible 16mm2 conductor to earth.
    Remind the client to check condition often

Similar Threads

  1. The next public protector
    By Citizen X in forum South African Politics Forum
    Replies: 4
    Last Post: 12-Aug-16, 12:56 PM
  2. SURGE ARRESTORS
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 24-Apr-15, 10:36 PM
  3. Surge Damage
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 22-Dec-14, 12:49 AM
  4. Replies: 0
    Last Post: 10-Jun-13, 01:20 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •