    Maybe someone can explain the following.

    You do an inspection on a house where the lights circuits are wired with open PVC wiring with porcelain cleats in the attic. It's not double insulated wire. It's in good condition and passes all the tests. I give it a pass, however, I must fail the installation because of 1 inch of open wire at a gu downlight connection.

    I cannot blame the client for thinking that I'm an idiot.

    My question is. What's the difference between the open wiring supported by porcelain cleats and the 1 inch of open wiring at the downlight ?

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    I agree and you made me think of that as well and I can not as yet fault it. Also open wiring is not recommended only.

    Keen to see what the others say but I'm with you in this as well.

    Also is a ladder considered a tool ?

    Sent from my CPH2197 using Tapatalk

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by Derlyn View Post
    Maybe someone can explain the following.

    You do an inspection on a house where the lights circuits are wired with open PVC wiring with porcelain cleats in the attic. It's not double insulated wire. It's in good condition and passes all the tests. I give it a pass, however, I must fail the installation because of 1 inch of open wire at a gu downlight connection.

    I cannot blame the client for thinking that I'm an idiot.

    My question is. What's the difference between the open wiring supported by porcelain cleats and the 1 inch of open wiring at the downlight ?
    Are you allowed to install open PVC wiring with porcelain cleats in the attic as part of a new installation?

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    No. I'm referring to existing installations

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dave A View Post
    Are you allowed to install open PVC wiring with porcelain cleats in the attic as part of a new installation?
    I would say Yes
    I would not do so or recommend that it be done as such but SANS 10142-1 makes mention of it - I have no idea why it does not say only if installed prior to 1980 or some such time as it was last allowed


    6.4.5 Open wiring
    NOTE Open wiring consists of single-core insulated conductors that operate at not
    more than 250 V to earth; however, this is not a recommended installation method for
    new installations.

    6.4.5.1 Open wiring shall not be installed
    a) under thatched or wood-shingle roofs,
    b) in parts of a roof space where the working height is less than 750 mm,
    c) in roof spaces that are intended to be used (or are used) for storage, unless
    the wiring is suitably protected against mechanical damage,
    d) within 1 m of a trap door unless the wiring is suitably protected
    against mechanical damage, or
    e) where it will be in contact with flammable material.

  6. Thanks given for this post:

    Derlyn (20-Sep-22)

  7. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    In that case seeing the cores of the FTE in a downlight I then deem ok, as long as not in thatch and those mentioned above.

    It's how I have justified it before

    Sent from my CPH2197 using Tapatalk

  8. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    However the 750mm thing for angled roofs means a lot of it needs to be protected, is double insulation of the FTE considered suitable mechanical protection ?

    Sent from my CPH2197 using Tapatalk

  9. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    So we agree the short piece between the FTE and the down light terminal is not a code violation?



    The only reason I would think it would be a fail, because the clamp is compressed on the single insulation.

  10. #9
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    I think it's fine, if it is considered open wiring however then if the roof to ceiling is less than 750mm then it needs mechanical protection.

    However the FTE pvc is not for mechanical protection so then it does not matter how we do the termination.

    So yes I think it is fine and will sign off of that.

    Unless it states that the single core PVC from FTE can not be shown then I will continue to do it.

    My only reasoning is that the second layer of the FTE is not for mechanical protection...

    Second to all this... Earthing of the downlight holder... The mechanism is cumbersome so been thinking can you just take a lead with a croc clip both ends and just clamp it ? I.e from the earth cable to the metal clip...

    It's not relying on twisting as the mechanical force of spring is there... It's shoddy but I can't fault this idea yet unless somwhere can say this idea is stupid with a reg hahahah.



    Sent from my CPH2197 using Tapatalk

  11. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    I think the answer is to use 1mm FTE where possible and to rather use a 3 way box when looping so that there's always only a single FTE to each GU10 fitting.

    Been playing around and making a connection with single FTE is quite doable however it becomes a challenge to get it done correctly with 2 FTE's hence the suggestion of a 3 way box.

Page 1 of 2 12 LastLast

Similar Threads

  1. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  2. open wiring
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 48
    Last Post: 29-Nov-14, 09:25 AM
  3. Exposed wiring in home bar lighting
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 14-Aug-14, 01:00 PM
  4. [Question] open wiring and cleats
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 24-Jan-12, 01:22 AM
  5. Vulnerability exposed
    By Dave A in forum Technology Forum
    Replies: 3
    Last Post: 05-Jan-07, 11:47 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •