  1. #11
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,587
    Thanks
    113
    Thanked 151 Times in 143 Posts
    As far as load shedding is concerned, I'm still convinced that my fridge safe together with contactor is the answer.

    My power comes on a couple of minutes after everyone else's and I'm sure the spikes caused by switching on are long gone by the time mine comes on.

    I have noticed that led lights are prone to failure because of spikes from loadshedding. How do I know this you may ask.? I have had many clients complaining that led lamps were blowing left right and centre. I suggested that when there's loadshedding to switch off the lights and only to switch them on again after the power has been turned back on. End of problem.

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    The spikes are recorded as load shedding is switched, on both, on and off. The bottom line is load shedding is doing a lot more damage than we identify. Its good busy for maintenance sparkies. A drive in a machine could cost in excess of R100 000 .

    Rather focus on your insurance, make sure you understand your cover and check that there is no clause which voids surges caused by anything other than lightning. The assessor will check the weather report for the day of the claim. Dont say you weren't warned, I see the insurance companies handing out proper wedgies to loyal customers who pay and think they are covered.

    Insurance companies are about collecting monthly revenue not paying out share holder profits.


    Quote Originally Posted by Derlyn View Post
    As far as load shedding is concerned, I'm still convinced that my fridge safe together with contactor is the answer.

    My power comes on a couple of minutes after everyone else's and I'm sure the spikes caused by switching on are long gone by the time mine comes on.

    I have noticed that led lights are prone to failure because of spikes from loadshedding. How do I know this you may ask.? I have had many clients complaining that led lamps were blowing left right and centre. I suggested that when there's loadshedding to switch off the lights and only to switch them on again after the power has been turned back on. End of problem.

  3. #13
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    The moral of the story, just like you pay the school teacher, teller at the bank and "insurance broker a monthly fee, make sure you get them to go through your policy step by step even if it means they must do a site visit and 5 hours to verify everything in the document and highlight everything you are not sure about. When that wall collapses or the drive pops, they will refer to the document you signed, its all there in the document.

  4. #14
    Bronze Member
    Join Date
    Feb 2018
    Location
    Pietermaritzburg
    Posts
    168
    Thanks
    12
    Thanked 4 Times in 4 Posts
    Thanks for the comments guys, lots of food for thought.

    My current policy only covers R10k which is nothing sadly. I was asking my broker to increase the cover and she mentioned that the insurance companies are loading premiums for higher cover, which can make it challenging for the lay man to accept.
    I was also told that the insurance companies are insisting on surge protection, but as far as I have read my policy does not stipulate this, but will confirm with the broker again.

    Seems we are getting screwed all round....

  5. #15
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,587
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Fortunately, I've never had insurance.

    Not once have I paid for other people's stuff to be replaced.

  6. #16
    Diamond Member Blurock's Avatar
    Join Date
    May 2010
    Location
    Durban
    Posts
    4,163
    Thanks
    758
    Thanked 891 Times in 739 Posts
    Blog Entries
    7
    Quote Originally Posted by Derlyn View Post
    As far as load shedding is concerned, I'm still convinced that my fridge safe together with contactor is the answer.

    My power comes on a couple of minutes after everyone else's and I'm sure the spikes caused by switching on are long gone by the time mine comes on.

    I have noticed that led lights are prone to failure because of spikes from loadshedding. How do I know this you may ask.? I have had many clients complaining that led lamps were blowing left right and centre. I suggested that when there's loadshedding to switch off the lights and only to switch them on again after the power has been turned back on. End of problem.
    The AUS-IoT Monitor (LoRa system) for electricity can be useful to prevent/reduce spikes. We can program the electricity meters in a complex to switch on in phases instead of all the units at the same time. That seems to work well for our customers.
    Click image for larger version. 

Name:	IMG_20201201_160949.jpg 
Views:	197 
Size:	30.6 KB 
ID:	8670
    Excellence is not a skill; its an attitude...

  7. #17
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Quick one on SPDs... I tried to look at manuals but can't find.

    What size conductors do we use ??

    So if the SPD does not have an integrated fuse then we need to have Circuit breaker before the SPD, so I then assume if we use a 20A then 2.5mm is fine, but that's not a lot of amps.... So then we do 50A CB and 10mm cable and then I assume same size for the Earth ?

    I can not find any info on what size cable and then what size circuit breaker.


    Same goes with the N E bridge on the other thread... What size relay/ contactor and what's size CB ?

    Sent from my CPH2197 using Tapatalk

  8. #18
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Dylboy View Post
    Quick one on SPDs... I tried to look at manuals but can't find.

    What size conductors do we use ??

    So if the SPD does not have an integrated fuse then we need to have Circuit breaker before the SPD, so I then assume if we use a 20A then 2.5mm is fine, but that's not a lot of amps.... So then we do 50A CB and 10mm cable and then I assume same size for the Earth ?

    I can not find any info on what size cable and then what size circuit breaker.


    Same goes with the N E bridge on the other thread... What size relay/ contactor and what's size CB ?

    Sent from my CPH2197 using Tapatalk
    Normal rules apply with regards to wire size - Manufacturers instruction will specify
    If your CB is SP domestic 80Amps then that should protect most surge arrestors .

    Relay size - same story - normal rules apply - If you have a 5Kw inverter the rating would be at least 20Amps with a surge of 7Kw on a 40 Amp CB protection on incomer and 20 Amp or 32 on output

    Max PSSC is equal to Max Surge - rate accordingly

  9. #19
    Bronze Member
    Join Date
    Feb 2018
    Location
    Pietermaritzburg
    Posts
    168
    Thanks
    12
    Thanked 4 Times in 4 Posts
    Quote Originally Posted by Blurock View Post
    The AUS-IoT Monitor (LoRa system) for electricity can be useful to prevent/reduce spikes. We can program the electricity meters in a complex to switch on in phases instead of all the units at the same time. That seems to work well for our customers.
    Click image for larger version. 

Name:	IMG_20201201_160949.jpg 
Views:	197 
Size:	30.6 KB 
ID:	8670
    Can these be installed in a private home? Please explain how this works if you don't mind.

  10. #20
    Diamond Member Blurock's Avatar
    Join Date
    May 2010
    Location
    Durban
    Posts
    4,163
    Thanks
    758
    Thanked 891 Times in 739 Posts
    Blog Entries
    7
    Quote Originally Posted by kavesh View Post
    Can these be installed in a private home? Please explain how this works if you don't mind.
    Yes, it can, providing there is LoRa cover in your area. It is ideal for residential and commercial complexes (including high-rise buildings) where one unit or section at a time is switched back on to prevent overload or spikes. We do not sell routers as it comes as part of the package where numbers warrant it. Routers are shared with the Worldwide LoRa Alliance. for a single user who is out of range, a mini LoRa wi-fi router is available. Unfortunately, at a cost.
    Click image for larger version. 

Name:	System.jpg 
Views:	191 
Size:	34.6 KB 
ID:	8672 Click image for larger version. 

Name:	Wi gateway.png 
Views:	194 
Size:	74.6 KB 
ID:	8673

    The AUS-IoT System allows Managing Agents to manage their utilities (water, gas & electricity) on a dashboard and an Android app for the tenants. Meters are read online and alerts for leaks and faults are sent via the system and email.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Aus system.jpg 
Views:	201 
Size:	35.0 KB 
ID:	8671  
    Excellence is not a skill; its an attitude...

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Lightning 6.7.7 and surge protection 6.7.6
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 13-Sep-22, 05:40 PM
  2. Surge protection
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 08:30 AM
  3. Lightning and surge protection insurance
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 25-Nov-21, 03:34 PM
  4. LED Ceiling mounted lights surge protection
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 01-Aug-21, 02:00 PM
  5. Lightning protection vs surge protection
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 28-Feb-20, 08:02 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •