    Issuing a COC for a property with solar and an invalid COC

    This is going to be interesting.

    We have a request to issue a COC for a property being sold.

    The property has a COC which was issued when the customer purchased the property, after reviewing it and doing a quick visual inspection, the COC is invalid (6 years old) not just because it is older than 2 years, the visual inspection identified quite a few code violations.

    To complicate things, the property has had a solar system installed, many years ago (about 4 years). No COC was issued at the time of installation and the system is not registered.

    The plan is to carry out an inspection report of the entire property including the solar system, identify any code violations and create a report with a quote to repair.

    How would you tackle this ?

    Throw in the towel and rather just walk away ?

    Just do what many people do, fill out a COC and send a bill for R1500.00, chances are nobody will even know the COC is invalid.

    Do the right thing and carry out an inspection report on the building, switch the bypass switch to grid and exclude the solar installation (because in theory you cant issue a COC for the solar because your didn't do it)

    Take on the full responsibility and carry out a full inspection report including the solar PV, because eventually all solar installations will be older than 2 years and if the property is sold you will need to address the problem.

    You thought life as a sparky was simple

  2. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    That saying lead by example, my plan is to do it right and share it so that we can take one step closer to sorting out this industry.

    There is an invalid COC and the last test was done more than 6 years ago.

    Step 1

    Create a job no. and open a test report/COC.

    This is where the wheels normally fall off, people think the cost to do the test report includes issuing the COC, we need to start by getting this right.

    A COC is only issued once the test report is completed and no code violations are identified.

    In my case there is a long list of code violations. The test report will be completed and list of the code violation with reference to the SANS regs will be attached to the quote.

    An invoice will be submitted for the test report which must be paid before the list is handed over (due to bad debts created thanks to the lack of public awareness).

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Step 2

    A site visit which will include creating sketches of the property and buildings, identifying all the electrical components and photos of any code violations. This will take at least half the day, before we even start the testing.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    We start by printing out a copy of the COC (annexure 1)/test report for scribbling on so that there are no mistakes ( the document is invalid is there is a mistake... you cannot correct and initial)

    Done forget to print out additional test reports in case there are more than 1 DB.

    Top left Test report for DB/supply ... Main Db (additional DB's will require additional test reports)

    Top right fill in the COC number and below the date of issue.

    Then you take a bright colour highlighter and draw a line through note 1 IN TERMS OF SOUTH AFRICAN LEGISLATION, THE USER OR LESSOR IS RESPONSIBLE FOR THE SAFETY OF THE ELCTRICAL INSTALLTION .

    Section 1 - Location

    Physical address: The dome.
    Name of building : Truman bubble

    Section 2 - Installation

    (tick) Permanent

    Type of elctrical supply system - This will depend on your location. TN-S in our part of town.

    Voltage: This site is 230 VAC

    Number of phases: (tick) one

    Phase rotation: clockwise

    Frequency: 50 HZ

    Main switch type: (tick) Switch disconnector (on load isolator)

    Number of poles: 2 (do you put 1 or 2 poles for a single phase installations) ?

    Current rating: 60 Amps

    A short - circuit/withstand rating: 2.5 ka (standard from our council on domestic installations)

    Rated earth leakage tripping current: (tick) 30 mA

    Is surge protection installed: no

    Is lightning protection installed: no

    Is alternate power installed: yes (this needs to be discussed in more detail due to the solar system and maybe a generator)

    Is any part of the installation a specialized electrical installation: no

    Is any part of the installation at a voltage higher than 1 KV : no

    To be continued...

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Section 3 - Description of the installation covered by this report.

    This is a section which should be discussed in great detail. I see way to many test report with absolute junk written in this section.

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Before we go into more details in section 3, I need to go back a few steps.

    For this example we have Sub DB's x 4, a pool DB, a gate DB and an outbuilding with both grid and inverter backup fed from a split sub DB.

    The pool DB feeds other stuff (you thought I would make the example simple ), so a supplementary test report is required.

    The gate DB also feeds other stuff, so it also requires a supplementary test report.

    The outbuilding is fed from the split sub DB, to another split DB, which has double pole combo breakers on the inverter plug circuit, the plug and light circuit are fed via a double pole combo breaker.

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This is why I keep going on about isolation procedures, when you add backup power to a property, it is so important to keep records of everything, to create sketches and log as much about the site as possible.

    I also create XL spreadsheet with all the information about the site from the meter road to the last DB in the circuit. the data includes the circuit, the breaker, cable size, the location of each item and even the load of the appliance connected to the socket outlet.

    When the COC is issued it has a 25 pages of documents attached.

    There is nothing worse than arriving on site and there is not even a single line diagram, throw in a battery bank boiling and degassing or a fire and you have proper chaos.

  8. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I need to take a step back and consider lightning and surge protection, even though the location may not require it, because there is a solar installation linked to the electrical installation, lightning and surge protection will need to be checked and the device test report (page 303) will attached to the either the original COC or the supplementary COC or both.


    We have already taken note of Annex Q and identified the area is a low risk area.

    "Annex Q (informative)
    A simplified risk assessment method to determine surge
    protection requirements"


    Now I ask the question will class II DC surge protection in the combiner box be adequate for this installation ?

    I thought I would be finished by lunch time, I haven't even left the office yet, still busy putting the test reports together, fortunately I have already have XL spreadsheet setup to collect all the data, so it is just a matter of filling in the blocks.

  9. #9
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    This is brilliant!

    How you do a test report is how I want to but 100% of the time the client says not gonna happen as all that will take me 3 or 4 days... Not all on site but doing the reports.


    There is so much wrong on these solar things and even though you may have not done it you will take responsibility... Same as you didn't build the house back in the day but you still then take responsibility.

    I tend to do inspection and maybe tests, send quote for repairs and then go have lunch and never hear from them but I made my bucks by making them pay first before I step foot on site...

    When you tell someone there house they loved is not safe they don't like it, or saying you have to pay to get the house sold where they probably took a knock does not go well.

    But I did digress of topic.

    This is a great thread.

    At the end of the day you need to satisfy you happy and get paid.

    And I think doing line drawings of the property should be done, like in the electric fence CoC.

    Sent from my CPH2197 using Tapatalk

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    And to think one needs to issue a COC everytime you change a burn't plug socket outlet.

Page 1 of 4 123 ... LastLast

Similar Threads

  1. [Question] Issuing a summons
    By Wendy Lilje in forum General Business Forum
    Replies: 0
    Last Post: 27-Oct-19, 01:31 PM
  2. [Question] Pastel Run-time error 380 Invalid Property value
    By PWEZ in forum Accounting Forum
    Replies: 7
    Last Post: 04-Apr-18, 03:02 PM
  3. runtime error 380 invalid property value
    By tax@pinfo.co.za in forum Accounting Forum
    Replies: 0
    Last Post: 28-Aug-15, 08:09 AM
  4. [Question] Issuing of CoC
    By siphom_3 in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 16-May-11, 08:03 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •