Thread: Socket outlet on cabtyre flex.

  1. #11
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ahhhh you are right... Fixed appliance is then any appliance actually that is fixed to the brick and mortar of the installation... Does not matter if plugged in or not.

    Then this thing of Isetech of being if it is fixed to the installation it must then comply.

    Glad this conversation happened thank you

    Sent from my CPH2197 using Tapatalk

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Derlyn View Post
    If you use cabtyre, don't forget to change the insulation colours on the ends. Brown to red and blue to black using tape or heat shrink and use bootlace ferrules to protect the conductor ends.

    Neglecting to do the above will make it non compliant.
    To date I have never seen anyone ever fit red tape or red sleeve to a brown wire or black to a blue wire.

    What I do see a lot is brown used for live - blue for neutral and green/yellow for the return/live for lights connected to PEC's.

    The only time I ever seen red tape used to identify a wire, red taped on the bare wire of FTE and surfix used for return/lives in lighting

    Bootlace ferrules, the only place they are used is for control wires in panels.

  3. #13
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Isetech View Post
    To date I have never seen anyone ever fit red tape or red sleeve to a brown wire or black to a blue wire.

    What I do see a lot is brown used for live - blue for neutral and green/yellow for the return/live for lights connected to PEC's.

    The only time I ever seen red tape used to identify a wire, red taped on the bare wire of FTE and surfix used for return/lives in lighting

    Bootlace ferrules, the only place they are used is for control wires in panels.
    Then it will not comply and you cannot sign it off


    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142.
    Flexible cords with cross sectional
    area less than 1 mm2 shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules
    to prevent the strands from being cut off
    in terminations

  4. #14
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by GCE View Post
    Then it will not comply and you cannot sign it off


    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142.
    Flexible cords with cross sectional
    area less than 1 mm2 shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules
    to prevent the strands from being cut off
    in terminations
    I agree 100 %, but the reality is that nobody seems to comply. One of the audits we have been busy with, was signed over by a member of an associassion (who you would think, would know better) after reporting the member we still found silly issues like this on site

    At least if it is dodgy cardboard electricians and DIY jobs, they might not know any better, but when qualified IE's and MIE's registered with the DOL and an associassion are signing off jobs like this, it becomes a big problem. It indicates that the responsible person has sent unskilled staff to site or not been to site and carried out a thorough test report.

  5. #15
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Every site I have been to where I am not the spark there the owner or the IE is never ever there as generally they the owner and it shows with the amount of F ups that come later on...

    Sent from my CPH2197 using Tapatalk

Page 2 of 2 FirstFirst 12

Similar Threads

  1. 6 Amp socket outlet and plugtop.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 20-Aug-22, 03:56 PM
  2. Replacing a metal socket outlet with a plastic socket outlet
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 18-Jun-22, 04:17 PM
  3. Socket outlet above hob
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 14-Nov-18, 02:57 PM
  4. socket-outlet question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 28-Aug-16, 03:06 PM
  5. Socket Outlet Confusion
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Nov-14, 11:57 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •