    Socket outlet on cabtyre flex.

    Hi All

    Sitting with a situation.

    A socket outlet in braai area has been wired with cabtyre flex.

    It is wired with 1,5mm on a 16A circuit breaker. ( that's in order )

    The total length of this circuit is 8 meters.

    Problem is that this cabtyre flex runs above a ceiling under a flat roof, so cannot be replaced without either removing the roof sheets or ceiling boards to gain access.

    I have tried finding a regulation that makes the above scenario non compliant, without success.
    I cannot find anything that bans the use of cabtyre.

    Is it compliant ?

    What sayeth the other toppies ?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi

    Flexible cords/cabtyre is allowed in an installation must must comply to the regs pasted below.
    The job should still be done as if it was Twin and earth , in other words not plugged in on a plug top but as part of the installation .
    That is the way I read it
    Using Cabtyre is not a license to do the work like a cowboy



    3.8.3
    flexible cord
    cable of which
    a) the nominal cross-sectional area of each conductor does not exceed
    4 mm˛, and
    b) each conductor consists of strands of diameter less than 0,31 mm

    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142. Flexible cords with cross sectional
    area less than 1 mm2 shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules to prevent the strands from being cut off
    in terminations


    6.3.7 Joints and terminations
    6.3.7.1 Joints and terminations of cables, cores and conductors shall be
    made in accordance with manufacturers' instructions or the appropriate part
    of SANS 10198-10 and SANS 10198-11.
    Flexible cables shall only be joined using termination boxes, cable couplers or
    manufacturers’ jointing kits.
    All joints shall be accessible, protected against strain, and protected in
    accordance with 5.2.1, except for joints made and sealed permanently and
    intended to be maintenance free.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Thanks GCE.

    When I did the inspection, it was plugged into a socket outlet in the garage.

    I then had 2 options.

    1. Either remove the socket outlet at the braai or
    2. Make it compliant.

    I chose the latter by removing the plug top in the garage, connecting it directly to the plug circuit and changing the 20A circuit breaker to 16A.

    Thanks for the reply. It seems as if I'm in the clear. Dealing with an unreasonable buyer who got another spark to check my Coc and he was advised by hi's guy that the cabtyre is not compliant.

    The attorney who did the transfer is now asking questions.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Derlyn View Post
    Thanks GCE.

    When I did the inspection, it was plugged into a socket outlet in the garage.

    I then had 2 options.

    1. Either remove the socket outlet at the braai or
    2. Make it compliant.

    I chose the latter by removing the plug top in the garage, connecting it directly to the plug circuit and changing the 20A circuit breaker to 16A.

    Thanks for the reply. It seems as if I'm in the clear. Dealing with an unreasonable buyer who got another spark to check my Coc and he was advised by hi's guy that the cabtyre is not compliant.

    The attorney who did the transfer is now asking questions.

    I was also put in this position a couple months ago, My customer purchased a property with a bunch of extension cords feeding, outside lights, extension cords feeding the gate wire with comms cable in the same pipe, a long list.

    As pointed out by the person who issued the COC, everything had plug tops and therefore was not part of the electrical installation. My response was that is fine so long as nothing is secured to the building.

    However this is where it gets interesting, firstly you cannot run a power cable in the same conduit as a comms cable, even if it is plugged into the wall.

    My argument wasnt about the cabtyre hanging everywhere plugged into socket outlets, my argument was that all the fixtures were not working once I removed all the extension cords cut it off at the fixture and told them to return all the extension cords to the seller.

    It wasnt the fact that they had used 1.5 mm cabtyre to wire the building, the problem was the 30 amp circuit breakers feeding the socket outlets which were wired in 4 mm house wire.

    No mechanical protection at the base of the wall where it entered the conduit under the driveway.

    No supports for the cables hanging between the garage and the house, more than 3m gap.

    The exposed skrewits used to connect the cabtyre at various points.

    The damaged light fittings secured to the building (the only part secured to the building)

    There seems to be this misunderstanding about the use flexible cable like cabtyre, aquau cable, trailing cables etc. I have wired up machines in factories using trailing cable.

    The way I see it, if you plug a plug top into a socket outlet and just hang it loosely around the building, thats fine, however as soon as you secure any part of the cabtyre or the appliance to the building, be it the roof, the wall or floor, it now becomes a fixture and must be compliant. Right or wrong I dont really care, because at the end of the day I am going to sit with the problem when the buyer my customer decides to sell.

    if you sell one of my customers a property and you have cabtyre hanging all over the building and wrap the cabtyre around the rafters loosely, no problem, just dont secure any part of it to the building.

    As we all know the standards are min. guidelines, if you are a buyer you can expect some sort of standard and min requirements. This is why I always insist on the buyer getting me to check the property prior to signing the transfer documents, at that point we can decide what is acceptable and use the regs as a min standard.

    Another example is damaged covers, you dont have to replace damaged covers if it is just cracked, but if you take into consideration what it is going to cost to replace all damaged covers and any other you find on the property, it might impact the price.

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    In short you can do whatever you want to do with cabtyre that is plugged into a socket outlet and not secured to the building, you can even use a 0,5 mm cabtyre, hang it across the pool while you cut the grass with an electric mower, you can even do dumb things like connecting all the 230VAC strip lights hanging over the pool net in the pool, nobody cares.

    Just dont make it a fixture by mounting it or securing it to the side of the pool or connect it to the gate or pool DB or security lights.

  6. #6
    Full Member
    Join Date
    Aug 2018
    Location
    pretoria
    Posts
    35
    Thanks
    0
    Thanked 0 Times in 0 Posts

    making security lights a fixture

    hi there isetech please allow me to understand what you are saying,the security lights will of course be fixed to a wall
    does this mean that this will make the whole setup cabtyre ,plugged into a socket outlet cabtyre hanging loose unacceptable?
    and because the light now is fixed to the wall it has to be deemed as part of the installation and thus cannot be excluded from the coc?
    secondly may i just ask that should a cable be running through an inaccesible area ex a flat roof where there may be connection boxes and therefore perhaps unseen connections what will the procedure be on this .those connections could be open but my meggar and multimeter might not pick up any faults ?

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Forgot to mention.
    Only if the buyer is presently living in the house do I sometimes involve them, otherwise, never.

    The safest way to CYA is to go by the book. It then doesn't matter how unreasonable or difficult the buyer is, you're covered.

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    If you use cabtyre, don't forget to change the insulation colours on the ends. Brown to red and blue to black using tape or heat shrink and use bootlace ferrules to protect the conductor ends.

    Neglecting to do the above will make it non compliant.

  9. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Derlyn View Post
    If you use cabtyre, don't forget to change the insulation colours on the ends. Brown to red and blue to black using tape or heat shrink and use bootlace ferrules to protect the conductor ends.

    Neglecting to do the above will make it non compliant.
    To date I have never seen anyone ever fit red tape or red sleeve to a brown wire or black to a blue wire.

    What I do see a lot is brown used for live - blue for neutral and green/yellow for the return/live for lights connected to PEC's.

    The only time I ever seen red tape used to identify a wire, red taped on the bare wire of FTE and surfix used for return/lives in lighting

    Bootlace ferrules, the only place they are used is for control wires in panels.

  10. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Isetech View Post
    To date I have never seen anyone ever fit red tape or red sleeve to a brown wire or black to a blue wire.

    What I do see a lot is brown used for live - blue for neutral and green/yellow for the return/live for lights connected to PEC's.

    The only time I ever seen red tape used to identify a wire, red taped on the bare wire of FTE and surfix used for return/lives in lighting

    Bootlace ferrules, the only place they are used is for control wires in panels.
    Then it will not comply and you cannot sign it off


    6.1.11 Where flexible cords are used as part of the electrical installation, the
    selection, installation and colour identification (see 6.3.3) shall be done in
    accordance with this part of SANS 10142.
    Flexible cords with cross sectional
    area less than 1 mm2 shall not be permitted.
    6.1.12 Where flexible cords are used, the strands of the conductors shall be
    mechanically protected with ferrules
    to prevent the strands from being cut off
    in terminations

Page 1 of 2 12 LastLast

Similar Threads

  1. 6 Amp socket outlet and plugtop.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 20-Aug-22, 03:56 PM
  2. Replacing a metal socket outlet with a plastic socket outlet
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 18-Jun-22, 04:17 PM
  3. Socket outlet above hob
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 14-Nov-18, 02:57 PM
  4. socket-outlet question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 28-Aug-16, 03:06 PM
  5. Socket Outlet Confusion
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Nov-14, 11:57 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •