    6 Amp socket outlet and plugtop.

    Question.

    Lighting circuit. Wired with 1,5mm wire. 15 Amp circuit breaker. So far, so good.

    There's an extractor fan in bathroom wired in parrallel with bathroom light. No isolator for fan.

    Plan is to install an end box with 6A socket outlet and fit a plugtop on fan chord.

    My question is ...... one now has a socket outlet rated at 6 Amps protected by a 15A circuit breaker.

    Acceptable ?

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    I would say yes as most lighting circuits where the 6A is used is fed off a 15A. I mean even our normal 16A sockets are fed from a 20A CB

    One thing to also check is if the 6A needs to be on ELU, I don't think so but worth a check

    Sent from my CPH2197 using Tapatalk

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    6.14.1.5 A lighting circuit that incorporates 6 A or 16 A partially dedicated
    socket-outlets socket-outlets in accordance with 6.14.1.4 shall be protected
    by a circuit-breaker of not exceeding 20 A.

    Sent from my CPH2197 using Tapatalk

  4. Thank given for this post:

    Derlyn (18-Aug-22), Isetech (18-Aug-22)

  5. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,630
    Thanks
    116
    Thanked 153 Times in 145 Posts
    Thank you, brother.
    That's the reg I needed.

    As far as ELU is concerned, in all my years I have never wired lights through ELU, however, that is changing because of the ceiling fan issue. I have yet to see a ceiling fan wired through a double pole isolator that is within arms reach of the fan, so we now just wire the lights through the ELU in order to take care of that one.

  6. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Dylboy View Post
    6.14.1.5 A lighting circuit that incorporates 6 A or 16 A partially dedicated
    socket-outlets socket-outlets in accordance with 6.14.1.4 shall be protected
    by a circuit-breaker of not exceeding 20 A.

    Sent from my CPH2197 using Tapatalk
    We need more youngsters who are learning from this forum, to start getting actively involved and posting responses like this.

    If one person smiles, its starts rubbing off on everyone

  7. Thanks given for this post:

    Dylboy (18-Aug-22)

  8. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by Derlyn View Post
    Thank you, brother.
    That's the reg I needed.

    As far as ELU is concerned, in all my years I have never wired lights through ELU, however, that is changing because of the ceiling fan issue. I have yet to see a ceiling fan wired through a double pole isolator that is within arms reach of the fan, so we now just wire the lights through the ELU in order to take care of that one.
    Pleasure Uncle

    Yeah these fans with lights and ELU and isolators is quite a pain, especially when there is a N and E fault on the circuit hahah.

    Sent from my CPH2197 using Tapatalk

  9. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by Isetech View Post
    We need more youngsters who are learning from this forum, to start getting actively involved and posting responses like this.

    If one person smiles, its starts rubbing off on everyone
    100% agreed ! In sport if you play with people better than you you raise your own game too. Also as you say a smile is contagious

    Sent from my CPH2197 using Tapatalk

  10. #8
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    GCE inspires me a bit with his quick reg finding and understanding. I have now put my book in the car as well to use aswell as I have the PDF to quick search. I find a book I have all my notes so extra handy

    Sent from my CPH2197 using Tapatalk

  11. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,630
    Thanks
    116
    Thanked 153 Times in 145 Posts
    2 socket outlet questions.

    1)

    6.15.2.1 says that unless otherwise allowed in SANS 10142, socket outlets rated at less than 16A may not be used in an electrical installation.

    I am aware that according to 6.14.1.4 and 6.14.1.5 they can be used in lighting circuits.

    Without having to read through the whole book, are there any other applications where a 6A socket outlet is allowed ?


    2) Are there any regulations stating that a metal socket outlet must be used for certain applications in a domestic installation ?

    I have someone that insists that the under counter plug for hi's gas stove must be metal. I cannot find anything in SANS regarding this.

  12. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,365
    Thanks
    38
    Thanked 323 Times in 271 Posts
    Without having to read through the whole book, are there any other applications where a 6A socket outlet is allowed ?
    Is allowed under 6.16.4.3 for extraction fans on a Luminaire circuit -
    There used to be a statement made or an interruption that said luminaires only and I think it came from 6.14.1.4b - feeds one luminaire only

    6.16.4.3 Extraction fans
    Where an extraction fan supply is switched with a luminaire, it shall be
    connected to the switched portion of the light circuit, provided that the fan
    circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
    SANS 164-2-2 socket-outlet or a switch disconnector.


    6.14.1.4 In a lighting circuit, a luminaire that is in a false ceiling or in a roof
    space 4 m above the floor where there is no ceiling, or in a floor cavity, or in a
    wall cavity, or in a similar position, may be fed from a socket-outlet which may
    be unswitched and not protected by earth leakage protection, provided that
    the socket-outlet
    a) complies with SANS 164-3 or SANS 164-2-1 (PD-D type),
    b) supplies one luminaire only, not exceeding the rating of the socket-outlet,
    c) is accessible for maintenance purposes, and
    d) is within 3 m of the luminaire that it supplies.


    2) Are there any regulations stating that a metal socket outlet must be used for certain applications in a domestic installation ?

    I have someone that insists that the under counter plug for hi's gas stove must be metal. I cannot find anything in SANS regarding this.
    I have never seen that particular statement in the regulations - There was a statement made at one stage by the gas guys that any socket around an oven/hob must be metal but that was an opinion and not written anywhere in Electrical or gas regs

  13. Thank given for this post:

    Derlyn (18-Aug-22), Dylboy (18-Aug-22)

Page 1 of 2 12 LastLast

Similar Threads

  1. Replacing a metal socket outlet with a plastic socket outlet
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 18-Jun-22, 04:17 PM
  2. Socket outlet above hob
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 14-Nov-18, 02:57 PM
  3. [Question] Socket Outlet positionings
    By Smut in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 06-Mar-14, 01:33 PM
  4. unknown socket outlet
    By pipewood in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 09-Nov-12, 06:38 PM
  5. Socket outlet in bathroom
    By mlpotgieter in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Oct-11, 12:10 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •