    Garden ground lights tripping earth leakage

    Hi All

    Could really use some advise. Lets paint my situation. I recently had my 220v garden ground lights replaced by an electrician due to the previous lights not working from corrosion and tripping the earth leakage. There are 3 outdoor ground lights in total. These light are also connected to 5 outdoor wall lights. All the lights are fed through a normal plug outlet in my garage. The ground lights were disconnected from the wall lights due to the tripping issue.

    After the electrician installed the new ground lights everything worked fine but then after the first rain the lights tripped the earth leakage. The ground lights were encased in concrete and he initially used the original wiring for the ground light. He came back and changed out the cable for the ground light using surfix from flat twin and earth. He also used a waterproof connector for the surfix to ground light cable. The next time it rained it tripped again and I had to disconnect the ground lights again from the wall outside lights.

    He now wants to come back and move the feed from the socket outlet in the garage to a light switch that is not on earth leakage.

    My question is:

    Is it safe to have 220v outdoor ground lights on the light circuit that is not on earth leakage?
    If there was a puddle over these ground lights wont i get electrocuted due to the current issue?
    Should he not fix the fault that's causing the earth to trip. All the other outdoor lights are fine even in the rain, it's only when the ground lights are connected and it rains then it trips earth.

    Thank you very much

  2. #2
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    In my limited experience I would strongly advise against taking any circuit off earth leakage. The tripping is an indication of a problem. I suggest testing the lights one by one and by a process of elimination you will find the culprit. I've seen too many faulty circuits miraculously fixed by simply taking them off earth leakage.

  3. #3
    New Member
    Join Date
    Aug 2022
    Location
    Cape Town
    Posts
    5
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Andrew_van_Zyl View Post
    In my limited experience I would strongly advise against taking any circuit off earth leakage. The tripping is an indication of a problem. I suggest testing the lights one by one and by a process of elimination you will find the culprit. I've seen too many faulty circuits miraculously fixed by simply taking them off earth leakage.
    I think i know which one it is, one of the light has some condensation inside. Before they installed these new ground lights, i asked them to make 100% sure that the lights are waterproof.

    It puzzles me why a licensed electrician would take a shortcut to put these light off earth leakage. Would this pass coc if it had to be done?

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Lights do NOT need to be on earth leakage.

    Plug socket outlets and water heaters must be on earth leakage.

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,060
    Thanks
    56
    Thanked 98 Times in 94 Posts
    Quote Originally Posted by Derlyn View Post
    Lights do NOT need to be on earth leakage.

    Plug socket outlets and water heaters must be on earth leakage.
    Something to consider, outside lights sometimes require a little trenching.

  6. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Doesn't matter. I'm going by the book.
    Unless there are ceiling fans involved, luminaires do not need to be on earth leakage.

    The poster is trying to fault the electrician for wanting to connect the lights to the lighting circuit. Nothing illegal doing that.

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,526
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Movo View Post
    All the other outdoor lights are fine even in the rain, it's only when the ground lights are connected and it rains then it trips earth.

    Thank you very much
    That's probably because all the "other" outdoor lights are not on earth leakage. Nothing illegal or wrong with that.

  8. #8
    New Member
    Join Date
    Aug 2022
    Location
    Cape Town
    Posts
    5
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Derlyn View Post
    That's probably because all the "other" outdoor lights are not on earth leakage. Nothing illegal or wrong with that.
    If you read the post, i said that ALL the outdoor lights are connected on the same plug and did not trip prior. Im not trying to fault anyone, these are ground lights that are directly infront of my garage. I dont want myself or my kids to get electrocuted.

    In some countries outdoor lights have to be on a RCD. I want to know if what he is doing is safe not accepted practice. Based on the 1st response i got, i thought he was taking a shorcut, can anyone else confirm becase what i got now is 2 opposing views

  9. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,663
    Thanks
    3,309
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by Movo View Post
    In some countries outdoor lights have to be on a RCD. I want to know if what he is doing is safe not accepted practice. Based on the 1st response i got, i thought he was taking a shorcut, can anyone else confirm becase what i got now is 2 opposing views
    Derlyn is correct in that South African standards allow luminaires to not be on RCD/earth leakage protection. From a safety point of view, what will be critical is that any exposed conductive surface (any exposed metal part) is adequately earthed. That way, even if there is a full short between live and the conductive part, there will be sufficient current to trip the overcurrent protection without the part being at an unsafe potential voltage.

  10. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 308 Times in 260 Posts
    Quote Originally Posted by Movo View Post
    If you read the post, i said that ALL the outdoor lights are connected on the same plug and did not trip prior. Im not trying to fault anyone, these are ground lights that are directly infront of my garage. I dont want myself or my kids to get electrocuted.

    In some countries outdoor lights have to be on a RCD. I want to know if what he is doing is safe not accepted practice. Based on the 1st response i got, i thought he was taking a shorcut, can anyone else confirm becase what i got now is 2 opposing views
    I agree that the lights do not need to be on Earth Leakage .

    You talk ground lights - Are these the buried type that shine up ?
    Is it a sealed unit ? can you post a pic

Page 1 of 2 12 LastLast

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. Oven tripping earth leakage
    By S.A.M. in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 12-May-21, 10:06 AM
  4. Earth leakage tripping with no load ?
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 21-Oct-20, 07:16 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •