Thread: Garden ground lights tripping earth leakage

Threaded View

Previous Post Previous Post   Next Post Next Post
  1. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Talking about earth leakage, lights, wiring to the lights, installations methods, etc.


    6.4.4 Buried cables
    6.4.4.1 Unarmoured cables may be buried if they are insulated and sheathed.
    If unarmoured insulated cables are buried at a depth of
    a) less than 0,5 m, they shall be enclosed in conduit or otherwise
    mechanically protected (for example, in the case of paving or concrete)
    (see also 6.5), or protected by an earth leakage protection device with a
    rated earth leakage tripping current (rated residual current) IΔn not
    exceeding 30 mA, or

  2. Thanks given for this post:

    Derlyn (21-Aug-22)

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. Oven tripping earth leakage
    By S.A.M. in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 12-May-21, 10:06 AM
  4. Earth leakage tripping with no load ?
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 21-Oct-20, 07:16 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM