    Quote Originally Posted by GCE View Post
    I agree that the lights do not need to be on Earth Leakage .

    You talk ground lights - Are these the buried type that shine up ?
    Is it a sealed unit ? can you post a pic

    Thanks for the feedback all. I asked for lights that are waterproof due the old lights having water in them, corrosion and tripping but these can be opened to change the bulb

    These lights are brand new and the old lights that these replaced were identical. Click image for larger version. 

Name:	IMG-20220820-WA0001.jpg 
Views:	468 
Size:	61.1 KB 
ID:	8607

    For now they are disconnected from the outdoor light circuit. The other lights are on the walls and those are fine. Its only these in ground lights that trip when reconnected.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG-20220820-WA0002.jpg 
Views:	445 
Size:	62.5 KB 
ID:	8608  

  2. #12
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    It would appear that the lights are getting moisture in them

    We have found that they only way to keep moisture out of them is to use silicone paste, not silicone sealer, on the rubber seals and gland seals - The paste to rubber is like Dubbin to leather
    Silicone sealer tends to shrink when it gets cold and allows water to stream in.

    The 2nd thing that needs to be done is to excavate a hole the size of a 5 litre paint can or bigger, depending on the soil, below the uplighters and fill with coarse stone and then fit the uplighters. This allows for any water to soak away and not sit around the light fitting. When a light is on it gets warm and as soon as it is switched off it cools down and sucks water in , how or where is always a mystery - The stone trick generally works but if the soil has a lot of clay you always run the risk of getting water into the fitting .The only way is to have drainage to keep the fittings out of a " pool " of water from underneath.

    The look the fittings give in lighting up is always aesthetically pleasing but from a practical point of view a nightmare for installation

  3. Thanks given for this post:

    Movo (21-Aug-22)

  4. #13
    New Member
    Join Date
    Aug 2022
    Location
    Cape Town
    Posts
    5
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you for the advise, I will definitely use this

  5. #14
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Talking about earth leakage, lights, wiring to the lights, installations methods, etc.


    6.4.4 Buried cables
    6.4.4.1 Unarmoured cables may be buried if they are insulated and sheathed.
    If unarmoured insulated cables are buried at a depth of
    a) less than 0,5 m, they shall be enclosed in conduit or otherwise
    mechanically protected (for example, in the case of paving or concrete)
    (see also 6.5), or protected by an earth leakage protection device with a
    rated earth leakage tripping current (rated residual current) IΔn not
    exceeding 30 mA, or

  6. Thanks given for this post:

    Derlyn (21-Aug-22)

  7. #15
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Maybe change the lamps from 230V to 12V and use a transformer at source of the incoming supply.
    In this way the moisture issue will not cause the ELU to trip, and 12V as a lower voltage will reduce any residual current flow due to the moisture in the fitting.
    Granted a good installation is still recommend to maintain a longer life of the fittings to keep as much water out as possible.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. Oven tripping earth leakage
    By S.A.M. in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 12-May-21, 10:06 AM
  4. Earth leakage tripping with no load ?
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 21-Oct-20, 07:16 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •