    Quote Originally Posted by Justloadit View Post
    Just to add into the mix here, what if the winding A-B was inverted, in other words when the transformer was wound, they used 2 secondaries, and then made a connection for the centre?

    Would you measure 5V between A-B and B-C?

    Now what would the voltage be between A-C - 10V or 0V?
    Then you would have a V-O-V transformer and it would apply the same as the generators.

    110V - 0V - 110V (A - B - C)

    A-C would be 220V

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post

    Click image for larger version. 

Name:	Scan_20220715_152314.jpg 
Views:	341 
Size:	26.2 KB 
ID:	8591
    Quote Originally Posted by Isetech View Post
    Then you would have a V-O-V transformer and it would apply the same as the generators.

    110V - 0V - 110V (A - B - C)

    A-C would be 220V
    The above picture marked as #1 is a V - 0 - V
    It has all to do with the phase of the voltages being measured.
    A - is the start of the winding, and ends at B
    B - is the start of the second winding, and ends at C.
    When the AC wave goes positive, it is in phase in both windings simultaneously, and you will measure the 10V between A and C

    The scenario I refer to, is that the first winding starts at A, and ends at B
    The second winding starts at C and ends at B.
    So when the AC wave goes positive in the A-B winding, the wave goes negative in the B-C so when you measure from A to C, you will measure 0V.

    Sometimes when a transformer has 2 secondary windings, and we wish to double up on the current, then it is very important to identify the start of each winding when you connect them in parallel, if not then you would be shorting the transformer out.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •