Thanks maby were missing one another.
I have noticed something in the field.
Refering to table 7.1 and reg 7.1.4.1
In zone 2 would one place an extractor fan that has
IPX4 protection be on earth leakage and not able to touch with standard test finger.
Or
IPX4 protection and be a class 2 appliance
Is the IPX4 necessary which is not on table 7.1.
It seems that they are saying you can connect as per table 7.1 only ,but then there is reg 7.1.4.1.
Table 7.1 — Conditions under which electrical equipment may be
installed in a bathroom
7.1.4 Selection and erection of electrical equipment
7.1.4.1 Degrees of protection
Electrical equipment shall have at least the following degrees of
protection against ingress of water:
in zone 0: IPX7;
b) in zone 1: IPX5;
c) in zone 2: IPX4;
d) in zone 3: IP21; and
e) outside zone 3 in the same room: IP21, except for a distribution board
Thanks
Sent from my CPH2197 using Tapatalk