    1 Pole + Neutral VS 2 Pole MCB's

    Hi folks
    Any difference between the two (assuming both have overload protection)?
    Thanks in advance
    AvZ

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 307 Times in 260 Posts
    You would not use an SPN on 2 live wires or output of a safety transforming.

    My feeling is SPN should not be used on an inverter so as to provide overload protection on both legs of the output

    SPN is fine anywhere you want protection on live and need to disconnect the neutral

  3. Thanks given for this post:

    Andrew_van_Zyl (04-Jul-22)

  4. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,054
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by GCE View Post
    You would not use an SPN on 2 live wires or output of a safety transforming.

    My feeling is SPN should not be used on an inverter so as to provide overload protection on both legs of the output

    SPN is fine anywhere you want protection on live and need to disconnect the neutral
    Why would you want to do that if the neutral on the output of the inverter is bonded to ground? I use the SPN on the input and output of the inverters we install.

    The only thing we will be changing in the future is the protection size and wire. Instead of using a 32 amp SPN, we will be fitting 40 amp (I dont know if you get 40 amp SPN). I will also be installing 10 mm wire from the DB to the inverter and 10mm back to the essential sub DB for 5 kva units. IF we install 8 KVA units, which are becoming more popular because they can be used with the new bigger panels, I will probably need 16 mm wire.

  5. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,266
    Thanks
    34
    Thanked 307 Times in 260 Posts
    Quote Originally Posted by Isetech View Post
    Why would you want to do that if the neutral on the output of the inverter is bonded to ground? I use the SPN on the input and output of the inverters we install.

    The only thing we will be changing in the future is the protection size and wire. Instead of using a 32 amp SPN, we will be fitting 40 amp (I dont know if you get 40 amp SPN). I will also be installing 10 mm wire from the DB to the inverter and 10mm back to the essential sub DB for 5 kva units. IF we install 8 KVA units, which are becoming more popular because they can be used with the new bigger panels, I will probably need 16 mm wire.
    There will be times when it is not bonded depending on the set up for short periods of time

  6. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,054
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by GCE View Post
    There will be times when it is not bonded depending on the set up for short periods of time
    That is why it is important to understand the inverter type and installation criteria. IF we install an Axpert type of inverter the output is always bonded. Now as we move into the Hybrid bi directional type, its is going to be interesting to see what happens when we run the tests in the workshop.

  7. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    SP+N breakers also have a staggered break sequence where neutral contact breaks last and makes first. This can also cause interesting problems under certain fault conditions when the neutral isn't bonded to earth.
    _______________________________________________

    _______________________________________________

  8. Thanks given for this post:

    Andrew_van_Zyl (15-Jul-22)

Similar Threads

  1. [Question] When is a double pole isolator required for a fan
    By ians in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 17-Feb-22, 07:36 AM
  2. Hammond pole attorneys
    By ians in forum General Chat Forum
    Replies: 13
    Last Post: 12-Oct-21, 09:14 AM
  3. Why double pole isolators
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 04-Sep-21, 09:41 AM
  4. THD on Neutral
    By lyndsay in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 27-Jul-20, 01:29 PM
  5. triple pole breaker for a single phase supply
    By washayag in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 28-Sep-15, 04:57 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •