    We move on to selecting batteries for the inverter, there a lot of calculation and explanations on the internet. What I want to focus on is the size of the inverter and the backup.

    I have'nt done any data logging using a lithium battery yet ( my demo will arrive soon), so I will only be able to do true tests once it arrives.

    I have done numerous tests using lead acid (gel batteries) which has got me thinking.

    IF you install a 3.6 kva (3600watt) unit with a 24 VDC 100 amp/hr of battery power, you can only backup about 400 watts to last a couple hours, anything over that will drain the batteries so fast that it no longer becomes a viable backup option.

    This got me thinking, why would I install a 5 kva unit with only 1 x 100 amp/hr (5kwh) battery, it just doesnt make sense. Surely it would make more sense to save money and buy a 3.6 kva and get 1 x 100 amp/hr battery. If you can only use 400 watts of the inverter power during load shedding.

    Something to be aware of: Sunsynk has different models for example here are the PV string data.


    3. TECHNICAL SPECIFICATIONS
     SUNSYNK-3.6K-SG01/03LP1

    PV String Input Data
    Max. DC Input Power 4680W
    PV Input Voltage 370V (100V~500V)
    MPPT Range 125~425V
    Full Load DC Voltage Range 240~425V
    Start-up Voltage 150V
    PV Input Current 11A
    No. of MPPT Trackers 2
    No. of Strings Per MPPT Tracker 1+1


     SUNSYNK-3.6K-SG02LP1

    PV String Input Data
    Max. DC Input Power (W) 7000W
    Voc Max. (V) 500V
    MPPT Range (V) 125~425V
    Full Load DC Voltage Range (V) 240~425V
    Start-up Voltage (V) 150V
    PV Input Current (A) 11A+11A
    No. of MPPT Trackers 2
    No. of Strings Per MPPT Tracker 1+1

  2. Thanks given for this post:

    Gene (04-Jul-22)

  3. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Tip

    We had a battery go into shutdown and we couldn't get it to start charging.

    The reason it went into shutdown, when it reaches 80% DOD or 20 % SOC, it doesn't switch off and stop discharging, in fact it drops rather quickly, unless you pull the fuse or switch off the battery, it will just keep dropping.

    Hopefully the battery doesn't drop to zero % DOD. The IP 65 manual indicates that you shouldn't recharge the battery in less than 12 hours, however the technical support will tell you to increase the charge amps. Maybe I need to re check the manual.

    You will notice a red fault light, you have to switch off the inverter and battery, try restart the battery and inverter, lower the cutout setting and low battery setting and wait for the inverter to normalize. IF it doesn't normalize and the red fault light keeps switching on, you pretty screwed.

Similar Threads

  1. Axpert vs Sunsynk
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 15
    Last Post: 15-Jul-23, 09:42 AM
  2. Understanding RSS and Feeds
    By duncan drennan in forum Technology Forum
    Replies: 0
    Last Post: 08-Jun-07, 09:26 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •