We move on to selecting batteries for the inverter, there a lot of calculation and explanations on the internet. What I want to focus on is the size of the inverter and the backup.
I have'nt done any data logging using a lithium battery yet ( my demo will arrive soon), so I will only be able to do true tests once it arrives.
I have done numerous tests using lead acid (gel batteries) which has got me thinking.
IF you install a 3.6 kva (3600watt) unit with a 24 VDC 100 amp/hr of battery power, you can only backup about 400 watts to last a couple hours, anything over that will drain the batteries so fast that it no longer becomes a viable backup option.
This got me thinking, why would I install a 5 kva unit with only 1 x 100 amp/hr (5kwh) battery, it just doesnt make sense. Surely it would make more sense to save money and buy a 3.6 kva and get 1 x 100 amp/hr battery. If you can only use 400 watts of the inverter power during load shedding.
Something to be aware of: Sunsynk has different models for example here are the PV string data.
3. TECHNICAL SPECIFICATIONS
SUNSYNK-3.6K-SG01/03LP1
PV String Input Data
Max. DC Input Power 4680W
PV Input Voltage 370V (100V~500V)
MPPT Range 125~425V
Full Load DC Voltage Range 240~425V
Start-up Voltage 150V
PV Input Current 11A
No. of MPPT Trackers 2
No. of Strings Per MPPT Tracker 1+1
SUNSYNK-3.6K-SG02LP1
PV String Input Data
Max. DC Input Power (W) 7000W
Voc Max. (V) 500V
MPPT Range (V) 125~425V
Full Load DC Voltage Range (V) 240~425V
Start-up Voltage (V) 150V
PV Input Current (A) 11A+11A
No. of MPPT Trackers 2
No. of Strings Per MPPT Tracker 1+1