Originally Posted by
GCE
I disagree with your statement - 6.9.1.2 requires a disconnector and 6.9.2.2 requires neutral to be disconnected in single phase supply .
I know they are different clauses but to me if you read section 6.9. the clauses are all relevant to each other
6.6.1.1 Each distribution board shall be controlled by a switch-disconnector
(see 6.9.4). The switch-disconnector shall:
6.9.1.2 If an installation consists of separate parts, each part shall be
controlled by a sub-main switch-disconnector to disconnect
a) that part of the installation, or
b) individual circuits and appliances.
6.9.2.2 In the case of a single-phase circuit, the disconnecting device shall
disconnect live and neutral