    3 phase supply, single phase inverter

    Hello

    With regards to a 3 phase house how does one go about installing an inverter which is single phase...

    I may be quoting a job for solar but competing against a quote for a single phase inverter and now wondering how does one do it.

    Do you make the whole house single phase ?

    If using the Sunsynk the excess solar feeds back to the non essential laods. But if those laods are on another phase then you can't.

    So do you make the whole house single phase ? If so what about the meter for when you on the grid and it's only pulling from one phase ?



    Sent from my CPH2197 using Tapatalk

  2. #2
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    131
    Thanks
    60
    Thanked 10 Times in 9 Posts
    Also keen to know.
    When I installed my gennie I bridged the 3 phases in the switchover box so the single phase gen supplies all 3 phases

  3. Thanks given for this post:

    Dylboy (30-Jun-22)

  4. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    I changed my house from 3 phase to single phase. There was no advantageous reason to maintain the three phase. Made the genny and inverter easier and cheaper to install, and take advantage of the back feed.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. Thanks given for this post:

    Dylboy (30-Jun-22)

  6. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I am still trying to figure this out, feedback and pass through.

    Feed back is controlled by the CT coil from the solar panels back to the non essential or grid side of the inverter or to export back to the grid.

    Pass through is the current that can be supplied to the essential load via the UPS/essential side , ie: an 8 kw can handle 12 kw.

    Still a bit sketchy with this information.

  7. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ah nice.

    I think all is fine to make it single phase. But only thing back of mind is the billing and phase balance of Eskom and there may be penalty fees for doing so.

    But if it's been done and no adverse effects of that sort then I think all fine.


    Sent from my CPH2197 using Tapatalk

  8. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @justloadit. Evening brother.
    Wracking my coconut 😁😁

    Please explain to this sparky what you mean by taking advantage of the backfeed.

    Thanks .. Derek

  9. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    @justloadit. Evening brother.
    Wracking my coconut 😁😁

    Please explain to this sparky what you mean by taking advantage of the backfeed.

    Thanks .. Derek
    Hi Derek,

    If you use the Sunsync or the Deye, and you rewire your DB into essential and non essential loads, where essential loads are fed through the inverter, then during the day if there is excess solar energy, that means that the batteries are fully charged, and the essential loads are drawing less energy than than is available from solar, then using the installed CT just after the DB incoming isolator, the inverter then feeds the excess available energy back into the non essential loads to reduce the energy from the grid to almost null if there is an over supply of solar energy..

    Its almost like having the inverter on the input of the DB, but not requiring to size the inverter for the full DB load.
    I think this is called backfeed.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  10. Thanks given for this post:

    GCE (01-Jul-22)

  11. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Justloadit View Post
    Hi Derek,

    If you use the Sunsync or the Deye, and you rewire your DB into essential and non essential loads, where essential loads are fed through the inverter, then during the day if there is excess solar energy, that means that the batteries are fully charged, and the essential loads are drawing less energy than than is available from solar, then using the installed CT just after the DB incoming isolator, the inverter then feeds the excess available energy back into the non essential loads to reduce the energy from the grid to almost null if there is an over supply of solar energy..

    Its almost like having the inverter on the input of the DB, but not requiring to size the inverter for the full DB load.
    I think this is called backfeed.
    Well explained explanation of the use on a true Hybrid - Going to steal it to use

  12. Thanks given for this post:

    Justloadit (01-Jul-22)

  13. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Which brings me to selecting the inverter size, why are customer offering 5 kva units used a a backup can only run at a small percentage of the available power.

    The same problem we have when connecting a 5 KVA or smaller generator to a main DB.

  14. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @Justloadit
    Thanks brother. Neat. So the more panels you have, the better, always.

    I'm having loads of fun with my teeny weeny setup. This weekend I'm installing 3 analogue ammeters. Amps from panels. Charging amps to batteries. Load amps.

    This will help me understand what is happening in real time without me having to guess.

    Cheers.

Page 1 of 2 12 LastLast

Similar Threads

  1. Changing 3 phase electric DB to single phase. (Switchover etc)
    By Janbez54 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 05-Jul-21, 07:59 AM
  2. Inverter diagram for one phase on 3 phase installation feeding 2 db’s
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 19-Aug-20, 06:44 AM
  3. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  4. triple pole breaker for a single phase supply
    By washayag in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 28-Sep-15, 04:57 PM
  5. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •