Thread: Which 48 volt lithium battery is the best

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Could the C rating be reduced to protect "seconds" (not off the production line) batteries?

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Isetech View Post
    Could the C rating be reduced to protect "seconds" (not off the production line) batteries?
    The BMS in the batteries, only provide 2 functions as far as I know.
    1 - If the battery voltage drops below a predefined value, it disconnects the battery from the load. Gets enabled when the charger is enabled
    2 - In the case of a short circuit, then the BMS will disconnect the battery from the load. I am not sure here but i think it is again enabled when the charger is enabled.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I see it is official, you get a 10 year warranty for your Sunsynk setup if you use the Sunsynk battery with the Sunsynk inverter, why would you you sacrifice a 10 year warranty and use any other battery?

  5. #5
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    40
    Thanks
    43
    Thanked 0 Times in 0 Posts
    I got a 10 year guarantee for a DYE battery connected to a luxpower inverter, very happy with it.

  6. #6
    New Member HGTesla's Avatar
    Join Date
    Jul 2023
    Location
    China
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Choosing the appropriate 48-volt lithium battery type depends on specific requirements and application scenarios. Ensuring compatibility with the inverter or solar power system and meeting specific needs is crucial.

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    When selecting the battery for your system, how would the C rating affect the design?

    From the little experience I have installing inverters, you never want your system to be pulling 100% @100 amps if you are using a 100 amp/hr battery, especially if you are using the system as a backup (UPS type). You would need a pile of batteries if that is the case, then 0.5 or 1 C wouldnt be a a priority.

    An example: If you are using it for critical/essential loads, which generally the case in SA, the system should not not be fully loaded at any point, you want the system to support your essential loads at any point of the day or night with at least 6 hours of support, preferably longer, but they budget would determine the support period. The longest life cycle would be the better option, not the higher C rating.

    Another example would be a small workshop. A battery which can handle the full discharge capacity for short bursts would be a good option, because you might be running small machine with motors which start up. You are looking for a system to keep the workshop flow.

    It all seems to keep going back to one thing, design for the application. The solar and inverter audits fails seem to point at bad design. Understanding and designing the system around the customers application seems to be the missing link.

  8. #8
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Isetech View Post
    When selecting the battery for your system, how would the C rating affect the design?

    From the little experience I have installing inverters, you never want your system to be pulling 100% @100 amps if you are using a 100 amp/hr battery, especially if you are using the system as a backup (UPS type). You would need a pile of batteries if that is the case, then 0.5 or 1 C wouldnt be a a priority.

    An example: If you are using it for critical/essential loads, which generally the case in SA, the system should not not be fully loaded at any point, you want the system to support your essential loads at any point of the day or night with at least 6 hours of support, preferably longer, but they budget would determine the support period. The longest life cycle would be the better option, not the higher C rating.

    Another example would be a small workshop. A battery which can handle the full discharge capacity for short bursts would be a good option, because you might be running small machine with motors which start up. You are looking for a system to keep the workshop flow.

    It all seems to keep going back to one thing, design for the application. The solar and inverter audits fails seem to point at bad design. Understanding and designing the system around the customers application seems to be the missing link.
    Agreed, full C in my opinion should be reserved for instantaneous requirement of any load for a short period of time.
    I usually like to cater for at least 6 hours of load on my battery pack, preferably 10 hours.
    At 10 ours it ensures longer battery life due to the reduced period of charge time at a high rate to bring the capacity up to cater for the constant load shedding experienced in recent days.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Selecting a solar lithium battery
    By Isetech in forum Energy and Resource Conservation Forum
    Replies: 36
    Last Post: 11-Sep-23, 10:28 AM
  2. Charging lithium batteries
    By ians in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 23-May-21, 06:15 PM
  3. Swopping out lead acid batteries with lithium
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 11-May-21, 08:07 AM
  4. 12 volt lighting
    By ians in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 13-Oct-20, 12:46 PM
  5. energy saving 12 volt or 230 volt downlighters?
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 14-May-12, 08:49 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •