Page 1 of 2 12 LastLast
Results 1 to 10 of 13

Thread: Surge arrestors

  1. #1
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts

    Surge arrestors

    If you install a T2 surge arrestor in a domestic property, do you connect it directly after the main switch, using a 16 mm wire and no fuse or,

    do you install a 32 amp mcb and wire it with 4 mm wire?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Isetech View Post
    If you install a T2 surge arrestor in a domestic property, do you connect it directly after the main switch, using a 16 mm wire and no fuse or,

    do you install a 32 amp mcb and wire it with 4 mm wire?
    Normally a surge arrestor has 125Amp protection rating requirement .Some are different.

    If it was 125Amp rating and my main switch is 80Amp protection , I would leave it at full rating.

    If you stick a 32 Amp C/Breaker in it may trip on a surge that it is trying to clamp and then letting the rest of the surges through which kind of defeats the object.
    I would rather let the surge arrestor take the surge to earth and if it is a big surge trip the 80Amp supply - That way I ensure the client is disconnected from any further surges .

  3. #3
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by GCE View Post
    Normally a surge arrestor has 125Amp protection rating requirement .Some are different.

    If it was 125Amp rating and my main switch is 80Amp protection , I would leave it at full rating.

    If you stick a 32 Amp C/Breaker in it may trip on a surge that it is trying to clamp and then letting the rest of the surges through which kind of defeats the object.
    I would rather let the surge arrestor take the surge to earth and if it is a big surge trip the 80Amp supply - That way I ensure the client is disconnected from any further surges .
    The big unit we install in the factories have 125 amp fuses and wired accordingly.

    I have decided to mount the unit next to the main switch and using the busbar at the top to feed the L of the surge arrestor which will have a 16 mm supply cable, which reminds me I must check the main switch is not identified line and load, because the line will be in the bottom. I will also fit a tag on the main cable identifying line and load.

    I am using a little T2 10 ka CBI unit.

    I am told the surge arrestor will not carry any load it is a transient over voltage protective device.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This is another topic which we should discuss in a lot more detail. I normally contact the specialist in JHB, but he has retired and only works as a consultant now.

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    The manufacturer indicated that no circuit breaker is required and a 16 mm wire connected to the top of the surge arrester and a smaller wire for the earth (no size indicated , so we will use a 6mm) would be the preferable way to wire it. Than k goodness I have a busbar on the top of the breakers which are not on earth leakage, so installing a 10 or 16 mm bridge across the top should be fine. The supply breaker is 60 amps.

    I think it might be batter to get it in writing.

  7. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,497
    Thanks
    138
    Thanked 696 Times in 594 Posts
    Blog Entries
    1
    Quote Originally Posted by Isetech View Post
    The manufacturer indicated that no circuit breaker is required and a 16 mm wire connected to the top of the surge arrester and a smaller wire for the earth (no size indicated , so we will use a 6mm) would be the preferable way to wire it. Than k goodness I have a busbar on the top of the breakers which are not on earth leakage, so installing a 10 or 16 mm bridge across the top should be fine. The supply breaker is 60 amps.

    I think it might be batter to get it in writing.
    What qualifications does the person have who passed this information to you?
    The earth wire is one of the key elements in the operation of a surge arrester.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Justloadit View Post
    What qualifications does the person have who passed this information to you?
    The earth wire is one of the key elements in the operation of a surge arrester.
    I suppose it is like asking the counter salesman at the wholesaler what size wire you need to connect a 7.5 kw motor.
    Last edited by Isetech; 18-Jun-22 at 08:37 AM.

  9. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,253
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Would you install a surge arrestor at the main DB and the essential supply sub DB (after the inverter)?

    I am wondering if it would be necessary after the inverter, considering the inverter offers a pure sine wave and should have some form protection built in.

    It is a requirement to install DC surge protection in a combiner box for the solar power.

  10. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    I would say no as you say the inverter does all that

    Sent from my CPH2197 using Tapatalk

Page 1 of 2 12 LastLast

Similar Threads

  1. Surge protection
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 08:30 AM
  2. Power surge and the earth spike
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 05-May-15, 11:17 PM
  3. SURGE ARRESTORS
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 24-Apr-15, 10:36 PM
  4. Surge Damage
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 22-Dec-14, 12:49 AM
  5. power surge insurance
    By murdock in forum General Business Forum
    Replies: 1
    Last Post: 13-Dec-10, 12:06 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •